Discuss TT earth, Dual RCD or RCBO and Main Switch in the UK Electrical Forum area at ElectriciansForums.net
Andy C
I have a replacement consumer unit coming upon which is currently off a TT system with a nice low reading on the earth. There is no chance of the DNO converting to TNCS. No SPD or AFDD as per client.
I intend fitting a new Dual RCD consumer unit.
I have researched this site and there was talk of the main switch being swapped out for a 100mA time delayed RCD. Albeit as I understand all this will protect is the internal wiring from the main switch to the RCDs. The use of the glands and cleating of mains tails would reduce the chance of any damage.
1/ I am led to believe that a dual RCD board would not protect all the circuits.
2/ I believe that a dual RCD would be permissible and would not lose any protection even if one RCD was to trip.
My questions are which is correct 1 or 2, i believe its 1, secondly would you still replace the main switch with a time delayed RCD.
Thanks in advance.
Hi - provided there are no “high integrity” circuits connected prior to the RCDs then no need for 100mA time delay RCD upfront, in my view. Glands and clamps yes by all means.
Guys I have sorted this now. The internal wiring on consumer units between main switch and RCDs is fine as long as the manufacturers cables are used. You also have to ensure the mains tails are in a gland and are cleated which I do anyway.
Reply to TT earth, Dual RCD or RCBO and Main Switch in the UK Electrical Forum area at ElectriciansForums.net
Need some advice, I have 7 static caravans to connect which need to be connected via TT 1. All the vans have a 30ma RCD main switch internally...
I'm in a questions asking mood tonight. I briefely looked at a job today and I need to recommend a board change but need to justify it. Firstly...
The earthing arrangement where the hot tub will be installed is formed in the TN-C-S system. I want to install the sub-main distribution circuit...
Hello Need to replace a distribution board in the next few weeks to allow for more circuits to be installed in January. Existing is a TT system...
Hi all, I am at odds on whether RCD protection is required on an SWA of 14 metres, clipped direct under flooring direct from CU to an exterior...