Discuss TT Eathing system to be installed in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
3
Will a TT earthing system be complicated to fit to a block of 6 flats and 1 communal area
And is it expensive
UKPN have told me this is there preferred option rather than a new supply from the road which would be very expensive
 
Will a TT earthing system be complicated to fit to a block of 6 flats and 1 communal area
And is it expensive
UKPN have told me this is there preferred option rather than a new supply from the road which would be very expensive
Gary, I read in one of your other posts it is currently TN-S but another you said there is no earth .... which is it?
 
Complicated, probably not.
Cost, impossible to calculate remotely. You need a registered electrician who is experienced in TT systems.
NOTE that changing from the current supply type to TT will have implications on the installations in the 6 flats and common area.
We’re recent EICRs carried out on all flats? If so, hopefully there won’t be major changes needed, but only your electrician can tell you that.
 
I think you need to employ the service of an electrician to visit and provide you with options that are suitable for the building.
with a TT earth, the local distribution boards for each flat may have to be upgraded to include rcd protection amongst other things.
 
It’s simple conceptually, but it all depends on the local conditions.
Factors include
- The cable route between the main incomer and a suitable site for an electrode.
  • How the distribution is presently arranged regarding mechanical protection
  • how and where it’s best to add the required RCD protection.
You need some quotes - this isn’t an abstract question - it relates to a specific property and installation so we can’t really guess complexity or costs.
 
I think you need to employ the service of an electrician to visit and provide you with options that are suitable for the building.
with a TT earth, the local distribution boards for each flat may have to be upgraded to include rcd protection amongst other things.
Snap! Unfortunately, after a lot of work by us both, I see that @Garyburger has another thread running on the same subject.
Wasted my time.
 
A bonded service isn't TN-S? Sounds like just main bonding, you need an electrician on this ASAP.

Some photos would really help. But you do need an electrician
A bonded service isn't TN-S? Sounds like just main bonding, you need an electrician on this ASAP.

Some photos would really help. But you do need an electrician
A bonded service isn't TN-S? Sounds like just main bonding, you need an electrician on this ASAP.

Some photos would really help. But you do need an electrician
These flats was built 50 years ago and it’s only come to light there is not a decent earth
My electric cert is 3 years old but it is only when UKPN done an earth test on the block it’s found it’s not adequate
I attach a small part of my test cert
 

Attachments

  • D1274E86-35FC-4323-97BE-079D5D2A5305.png
    2.4 MB · Views: 23
Will a TT earthing system be complicated to fit to a block of 6 flats and 1 communal area
And is it expensive
UKPN have told me this is there preferred option rather than a new supply from the road which would be very expensive
This question cannot answered accurately in any detail over an internet forum. In order to answer your questions you need the advice of an electrician who can come an survey the site first-hand. (as already been advised)
 
These flats was built 50 years ago and it’s only come to light there is not a decent earth
My electric cert is 3 years old but it is only when UKPN done an earth test on the block it’s found it’s not adequate
I attach a small part of my test cert
Yea thats not TN-S. Historically incoming metal services were at times used for an earth. But they've ticked the wrong box, that's not TNS. You need to honestly get off here and get some electricians in asap
 

Reply to TT Eathing system to be installed in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hello Need to replace a distribution board in the next few weeks to allow for more circuits to be installed in January. Existing is a TT system...
Replies
6
Views
1K
Need some advice, I have 7 static caravans to connect which need to be connected via TT 1. All the vans have a 30ma RCD main switch internally...
Replies
6
Views
856
Carrying out a EICR in a commercial setting. In the main intake room the DNO supply comes in and it states clearly this is a PME system. 5 years...
Replies
5
Views
1K
Hi all, what is the best way to configure surge protection in domestic dwellings when you have multiple consumer units? Does each consumer unit...
Replies
21
Views
4K
Afternoon all I am looking for some advice as on what to with the suppliers earth after a conversion to a TT system. Current issue is earthing...
Replies
10
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock