hi all,
Looking for opinions for a job I’ve been asked to do.
Supply to summer house\workshop approx 8m away. TT system as out in the sticks. They want a couple of sockets and lights so going to give them a 25amp supply
House cu is split load job which is full and dosen't have a 100ma main switch.
Current plan:
Split tails and install small cu with 100ma s type rcd and mcb at house end.
2 or 3 core swa buired direct to another cu in the summerhouse with 30ma rcd and mcbs as required.
no bonding required at summerhouse but add second earth rod depending on the readings.
Other way i thought of doing it to reduce the cost slightly was use a 30ma rcbo at the house and jused fused spur for the lights in the summerhouse.
any thoughts?