Discuss TT system earth cable size....... in the UK Electrical Forum area at ElectriciansForums.net
The size should be determined via the adiabatic equation.
Whilst he may be correct that 16mm is not required, there is no reason to remove it.
It’s TT earthing.
Your not going to get hundreds of amps of fault current flowing in the earthing conductor.
(Depending on Ra) but I doubt it’s any higher than the ccc of 2.5mm single which is why the table exists
Even at 10 ohms Ra that’s only 23 amps of fault current which is never going to blow the service fuse.
Hi guys
At a job doing a re wire and the electrician i was with is changing the earth cable over from 16mm to 6mm
He says as its a tt system that it only needs a 6mm.
Is this right?
I think there must be a reason why he's doing this as no one would remove a cable in this scenario just because a smaller cable would be acceptable..... ooops, sorry, 'conductor' :). Tell us more of the story Magnoliafan?
Reply to TT system earth cable size....... in the UK Electrical Forum area at ElectriciansForums.net
I am planning to go semi off grid with a victron and battery system. The system will be installed in an out building about 20 meters away from...
TNC-S main supply with 16mm swa supplying garage consumer unit from main consumer unit in house, then 4mm swa supplying pond equipment through...
Im starting a re-wire of a top floor flat, they have run an 16mm T&E with a 6mm earth from the ground floor to the 3rd floor feeding the CU...
Carrying out a EICR in a commercial setting. In the main intake room the DNO supply comes in and it states clearly this is a PME system. 5 years...
Evening everyone . Currently looking at pricing a job up . It’s a hot tub supply . Outside socket with a few spare ways in an outdoor cu . 10mm...