in a t.t system i have all way thought you need a 100mA s type dp rcd covering the whole installation
been to a job today and it is a standard board dp isolator and filled with rcbo's which yes they will protect as for high earth loop but they are only single pole am i right in my thought's
 
Electrical2Go - Online Electrical Supplier
This official sponsor may provide discounts for members
K

KFORDHUNTER

  • Thread Starter Thread Starter
  • #2
My thoughts are that if every circuit is protected by a 30ma rcbo what is the need for a 100ma main rcd. I thought the 100mA rcd was to protect all "other" circuits when you could still have circuits on mcb only.
 
B

beaver74

  • Thread Starter Thread Starter
  • #3
My thoughts are that if every circuit is protected by a 30ma rcbo what is the need for a 100ma main rcd. I thought the 100mA rcd was to protect all "other" circuits when you could still have circuits on mcb only.
yes but i am thinking that rcbos in general are single pole as apossed to double pole main rcd
 
in a t.t system i have all way thought you need a 100mA s type dp rcd covering the whole installation
been to a job today and it is a standard board dp isolator and filled with rcbo's which yes they will protect as for high earth loop but they are only single pole am i right in my thought's
This configuration of board is probably what the IET intended to be the norm with regard to 17th Ed compliance. Can`t see a problem with it myself.
 
Y

YTSOxford

  • Thread Starter Thread Starter
  • #5
Its a very expensive way of doing it tho! U can get DP RCBOs but they take up 2 modules; I used a 30ma to protect swa running a supply out to a garage.
 
I agree that a board full of rcbo`s is way too expensive for many jobs in the domestic sector - the dual rcd boards are far more viable. Cost aside, rcbo`s just take up too much room in the currently produced boards!
 
B

BillR3

  • Thread Starter Thread Starter
  • #7
Most manufacturers now make single module RCBO's, Merlin Gerin and Wylex being the ones that I use on a regular basis.
 
I was under the impression that rcbo's were all double pole.That is why you have to connect the neutral into them and why there is a curly blue
lead hanging out of them-all I have seen and used have also been one
module type.Incidently they can be bought for around 15 quid a pop.
 
The neutral on most rcbo`s is for functional purposes but is NOT usually switched, hence the single pole designation.
 
Instyle LED Lighting Specialists UK
This official sponsor may provide discounts for members

Reply to tt system with rcbo's in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net