iceman

hi i was doin a minor works 2day on a light circuit on a tt system i couldnt get a reading for Zs cos me metre tripped out to determin Zs do i mesure Ze witch wos 38.8 and me R1 + R2 wos 0.61 = 39.41 this dont seem rite to me cos the tapulated value for a 6A breaker is 7.67 any help would be great cheers ;-)
 
so im right by recording 39.41 for Zs aslong as theres an rcd in place if not id hav to put somethin the remarks collem sugesting action required?
 
Have a look at table 41.5 page 50 of BRB and reg 411.5

If there is no rcd for a socket circuit on a tt i use code 1 and for others i use a code 2 and if only one rcd is used for all circuits in a property i use code 4

I normally record the value i see although i beleive it is ok to record less than 1667

A value of 1667 is only ok if an rcd is used
 
Last edited by a moderator:
im this case thn the rcd used was a 100A main switch with a 30mA trip so would state in the collem tht requires improvement
 

Reply to TT sysyems in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Hi there, I'm Currently doing my design calcs for my college project and doing the actual Zs calculation. Formula is Zs= Ze (or Zdb) + (R1+R2)...
Replies
1
Views
1K
Firstly, please go easy as I'm still a trainee! Working on my L3 2365 I'm having trouble understanding the rationale behind adiabatics...
Replies
3
Views
763
SORRY FOR LONG POST. So i have my 2391-52 multiple questions coming up on Friday 13th, ( yeh i know) and was giving some things to study over by...
Replies
4
Views
2K
HELLO Im learner yet! i would like to know something about the TT system! if i would have an outbuilding installation, like sumer house!the main...
Replies
9
Views
2K
Hi all. The title is a slight red-herring to provoke a response.... Looking through previous threads here and elsewhere tells me that the formula...
Replies
22
Views
10K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock