hi i was doin a minor works 2day on a light circuit on a tt system i couldnt get a reading for Zs cos me metre tripped out to determin Zs do i mesure Ze witch wos 38.8 and me R1 + R2 wos 0.61 = 39.41 this dont seem rite to me cos the tapulated value for a 6A breaker is 7.67 any help would be great cheers ;-)
so im right by recording 39.41 for Zs aslong as theres an rcd in place if not id hav to put somethin the remarks collem sugesting action required?
Have a look at table 41.5 page 50 of BRB and reg 411.5
If there is no rcd for a socket circuit on a tt i use code 1 and for others i use a code 2 and if only one rcd is used for all circuits in a property i use code 4
I normally record the value i see although i beleive it is ok to record less than 1667
A value of 1667 is only ok if an rcd is used
im this case thn the rcd used was a 100A main switch with a 30mA trip so would state in the collem tht requires improvement
Reply to TT sysyems in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
Hi there, I'm Currently doing my design calcs for my college project and doing the actual Zs calculation. Formula is Zs= Ze (or Zdb) + (R1+R2)...
Firstly, please go easy as I'm still a trainee! Working on my L3 2365 I'm having trouble understanding the rationale behind adiabatics...
SORRY FOR LONG POST. So i have my 2391-52 multiple questions coming up on Friday 13th, ( yeh i know) and was giving some things to study over by...
HELLO Im learner yet! i would like to know something about the TT system! if i would have an outbuilding installation, like sumer house!the main...
Hi all. The title is a slight red-herring to provoke a response.... Looking through previous threads here and elsewhere tells me that the formula...
10K