Discuss two methods to verify a low ohm meter i think is not working properly? in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Welcome to ElectriciansForums.net - The American Electrical Advice Forum
Head straight to the main forums to chat by click here:   American Electrical Advice Forum

Use a known length and size of cable (GN3 page 104 Table A1), apply temperature correction factor (GN3 page 105 Table A2), calculate expected resistance, null leads, test cable, record resistance. Is recorded resistance same as calculated resistance?, yes :- meter is probably ok. no :- test another known length and size of cable. Still not the same. Send meter away to be re-calibrated.
 

Reply to two methods to verify a low ohm meter i think is not working properly? in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.