O

onfire25

Hi guys,

Would be greatful if i could pick a few brains.

Scaniro.

You get a call re shower not working so pop over.....take pull coard down and can see that the supply netural has overheated and started to melt the PVC!

On the pull coard terminal for the netural supply you can clearly see that it too has started to overheat!

Re made the cable off and connected back to a new 45A pull coard.

Test results

R1+R2=0.04
IR = >299Mohms L-E, N-E, L-N
RCD @ x1=43.7ms
RCD @ x5=11.8ms
Zs = TRIP

I'm using a Megger MFT1552 and it was set on no trip.

The shower is a Gainsborough 9 or 9.5Kw
Cable is 10mm
45A 60898-B MCB

The length of run of cable is about 13M

The RCD (80A 30mA) for that side of the board keeps tripping whilst trying to do the Zs at the pull coard.

Ramp test on RCD tripped at 25mA so not to worried about the RCD.....but would appreciate some thoughts re overheating netural and why i am not able to undertake a direct measurement of Zs.

I have taken a Ze reading and done Zs by calc but really want to do a direct......peace of mind and all that.

Any thoughts would be appreciated.
 
Will agree with that reason.....where im not able to get a direct measurement of Zs im probably over-reading that bit.

Any thoughts though re the Zs bit and tripping?
 
If it absolutely refuses to hold on the Zs test why not prove your CPC continuity with a wander lead between the shower and the MET, then as said enter the calculated figure on the SoTR.
 
well you`v got an R1+R2....so whats your problem?....go to the incomer and get yourself a Ze....then just calc it....
I got a Ze of 0.19 therefore by calc Zs=0.23......which is fine......call it ---- but i just want a direct measurement or know a logical reason for not being able to get one on a straight run of cable with no joints!
 
Some rcds seem to require a bit of resistance for some reason.connect about 1 metre of 1.5 flex at the circuit breaker disconnect shower circuit and see if the meter will do a loop test at the board.if you have the luxury of another meter cross reference the two. My megger likes some rcds better than my metrel and vice versa
 

Reply to Unable to to get a direct measurement reading for shower Zs in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

So was on a call out today and cooker circuit kept tripping the RCD. Disconnected at the board and at the cooker switch and IR’d the cable and...
Replies
9
Views
376
I've been fault finding an issue in a domestic property, the situation is as follows... RCD spur that is protecting outside sockets, This spur...
Replies
3
Views
1K
A few weeks ago I posted this in another thread...: The tripping kept occurring, so I went back and moved a likely candidate circuit to the...
Replies
2
Views
1K
Doing some testing today on a Wet Room installation. Fed from its own small CU. And consists of 2 x seperate 50A (for 10.5kw shower) circuits...
Replies
23
Views
3K
Hello, looking for some advice on 2 things please. Ive tested a ring main in a house with RCD protection, the results ive had are L-L .43 N-N...
Replies
24
Views
5K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock