O
onfire25
Hi guys,
Would be greatful if i could pick a few brains.
Scaniro.
You get a call re shower not working so pop over.....take pull coard down and can see that the supply netural has overheated and started to melt the PVC!
On the pull coard terminal for the netural supply you can clearly see that it too has started to overheat!
Re made the cable off and connected back to a new 45A pull coard.
Test results
R1+R2=0.04
IR = >299Mohms L-E, N-E, L-N
RCD @ x1=43.7ms
RCD @ x5=11.8ms
Zs = TRIP
I'm using a Megger MFT1552 and it was set on no trip.
The shower is a Gainsborough 9 or 9.5Kw
Cable is 10mm
45A 60898-B MCB
The length of run of cable is about 13M
The RCD (80A 30mA) for that side of the board keeps tripping whilst trying to do the Zs at the pull coard.
Ramp test on RCD tripped at 25mA so not to worried about the RCD.....but would appreciate some thoughts re overheating netural and why i am not able to undertake a direct measurement of Zs.
I have taken a Ze reading and done Zs by calc but really want to do a direct......peace of mind and all that.
Any thoughts would be appreciated.
Scaniro.
Test results
R1+R2=0.04
RCD @ x1=43.7ms
RCD @ x5=11.8ms
Zs = TRIP
Cable is 10mm
45A 60898-B MCB