Hi All

Got to install some underfloor heating in the kitchen and new conversion, i have installed these before but on a much smaller scale. Question is i have two heating mats at 10m2 each both together come to just over 15amps, is it ok to put these on a 16amp or do you think it mat be a bit to close ?

Also fcu is only rated at 13amps, which options do i have in ways around this ?

cheers paul
 
Thanks for response, I was planning on putting the 2 mats on one themostat as the kitchen
and conversion will be one room and the thermostat is capable of taking the 2.

If j have to radial circuits surely I would need 2 themostats ?
 
Last edited by a moderator:
If they both add up to 15amps how about a 20 amp radial through a 20 amp DP switch, as long as the single stat can handle the load , the only problem might be the floor probes for the two mats or could you run off of one ?
 
Thanks for that , I think that will be the better choice, as the heater is going to control one room . I think I can get away with just the one probe.
 
Or install in 2 circuits via a contactor and have the stat controlling the coil.
 
Thinking about it, it wouldn`t be a good idea to use one probe just in case the element where the probe is situated developed an open circuit fault, it would allow the other element to carry on heating up, without a stat/probe in that area to cut the power.
 

Reply to Underfloor Heating Question in the Australia area at ElectriciansForums.net

Similar Threads

Up until now I have steered clear of heating systems. I now have quite a bit of work with a builder and will be expected to deal with the...
Replies
4
Views
823
I've pretty much sussed out the wiring for the radiators and underfloor heating, thanks to help from the forum. I do have one more question...
Replies
6
Views
650
I have not had to do the wiring for a wet underfloor heating system before. I think I started a thread fairly recently and had some very good...
Replies
24
Views
2K
Hi there I need your opinion on this one, I need to fix mat 18sqm (200w). Client instead of one mat bought 2 mats (12sqm)+(6sqm) one thermostat ...
Replies
7
Views
799
Hi, this is a bit complicated. We installed two separate underfloor heating system in our downstairs area. One at 240V and according to the...
Replies
3
Views
961

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock