mjmarkey1967

Morning gents (and ladies)

I have a job the now at a hydro power station where the client is experiencing a loss in production and believes this is due to moisture ingress into underound electrical joints along the 3km route of the 10core 5 pair BS5308 Type 2 Part 2 hill instrumentation cable. These are supposed to be epoxy scotch cast joints according to the as-builts, which have northing and eastings also kindly provided, however the client doesn't want to entertain verifying the accuracy of the drawings by inputting the co-ordinates into a suitable GPS device and digging trial holes which I have previously suggested.

The electrical contractor has since went bust, and we have learned the complete route wasn't reticulated in ducting, obviously a £ saving measure on the contractors part.

I have tried the use of the Bicotest T625 time domain reflectometer on site to identify any changes of impedance at these joint locations but also had no joy. Loop continuity and megger testing was also carried out between cores and individual cores to earth and although IR ohmic values has degraded over time, all seems that it should still function as intended as a signal path.

Does any body else have any similar experiences to trying to locate such buried items or ideas how I can keep a long running client happy?

Many thanks in advance.
 
Last edited by a moderator:
sound like a nightmare, and can't realy advise since accessing the cable joints would be the best bet.
However if the test's are all clear, the issue might not be with the cable/joints.
does your client only have a problem after a good rain soaking?
 
All i can say is that it serves the client right!! On a project such as this, ALL cable joints should be accurately shown as to there location, on an overall site layout services drawing, and be also be marked on the ground with a propriety made for purpose concrete/stone marker. This should also be the case for underground cable routes, where ground markers will indicate routes, depths, number of cables and changes of direction etc,etc...

And now you know WHY this is normally a standard requirement on such high profile projects....
 

Reply to Underground Cable Joints - Location? in the Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock