- Reaction score
- 5,604
I am trying to understand 3 phase volt drop. I understand single phase VD.
Lets say we have a 70 meter run of 35mm, 5 core cable from the supply to the 3 phase consumer unit.
From the 3 phase consumer unit we have 1 x 16A triple pole MCB (so that's 16A per phase). which has a run of 12metres in 2.5mm SWA (5 core 70 degrees). Lets say it's going to a commando socket, just so it's easier to explain.
From the same consumer unit we have 1 x 20A single pole MCB which has a run of 15 meters, in 4mm SWA (3 core, 70 degrees). Let's say to a standard socket.
We'll assume max demand is 16A and 20A (no diversity)
VD from CU to standard socket = (20A x 15metres x 11 ) / 1000 = 3.3v
VD from CU to commando socket = (16A x 12m x 15) / 1000 = 2.88v
I'm not sure where to go from here. Do I use 36A as max demand and then just use the volt drop tables for 3 phase in order to find the VD between supply and CU?
If I did this it would be as follows....
VD from supply to CU = (36A x 70m x 1.1) / 1000 = 2.77v (to 2 dp)
Therefore highest VD is to the standard socket at 3.3v + 2.77V = 6.07v
The reason I am confused is because of the mixture of single phase and 3 phase equipment coming from the same CU.