- Reaction score
- 735
A while back a had an issue with a commercial install I had done for a family members unit
Long story short, 5x50w led floods controlled by 4 robus PIR detectors. Also a 3 way switch for option to turn off, perm on and PIR sensors.
I tested the circuit prior to any work and all the readings where good. I came across an issue where the RCD FCU that I had used on the perimiter trunking kept tripping. Unfortunatly I ran out of time on the original install.
I went back just before xmas to finish a few snags on other works and to look at this fault.
Disconnected the load from the JB and all my works tested fine. Good Zs and I/R over range.
Tested the circuit back to the board and gor a dead short between all conductors. Checked the board and there was 3 outgoing lives from the MCB. I should have confirmed this before I originally installed anything but all the figures were good so I thought it was safe to proceed.
I confirmed the line, neutral and cpc for the lights I have installed. The others I could not confirm so put them in a little JB next to the DB with a label.
The problem I have is I could not I/R test with the others disconnected because there was 20v on the circuit and my tester would not test. As soon as you reconnect the other 2 outgoing line and neutrals the 20v disappears and I can test but get a dead short. I tried line and neutral to earth and that was a dead short also.
I dont understand what was going on. I have left it for over the xmas period as they are closed however I'm still scratching my head.
Any help would be really appreciated.