It's 1.37 x 0.96
It's the zs your using temp correction with not the voltage
1.37 x 0.96 = 1.31

OSG says 1.1

I guess what you said to start with is the reason, they are using different conductor tempertures for their calculations, or something.

Thank you for your time, why they do not print the same information frustrates me, it makes learning very confusing.
1.37 x 0.96 = 1.31
1.31/1.2 = 1.096 or 1.1 ohms
The 1.2 is to adjust back to 70 degrees
I've made it too complicated just get your zs from bs 7971 and x it by 0.8 to get your max zs when testing at site temperature
 
So say if I measured Zs at 1.3ohms and looked at the table in the OSG and it said it should not be greater than 1.1ohms, should I be concerned? Or just ignore the OSG and use the values in BS7671
If the zs is too high when testing at site temperature then it will be safe to say it will be too high at cable operating temperature.
We can't test when cable is running at operating temp which is why we adjust our values for testing at site temperatures
 
the osg assumes a worst case of the cable operating at 70 degrees. except in some industrial situations, this is extremely rare. e.g. i once had a 16mm T/E running at 110A for 30 minutes. temp. did not exceed 40 degrees.
 
hnd in electrical engineering

i got that and i ain't that good. forgotten too much.
 
the osg assumes a worst case of the cable operating at 70 degrees. except in some industrial situations, this is extremely rare. e.g. i once had a 16mm T/E running at 110A for 30 minutes. temp. did not exceed 40 degrees.
Make you wonder if these cables actually can run at more amps in the different reference methods given by bs 7671 or they just play it too safe?
 

Reply to Understanding Zs values in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

I am a lecturer teaching electrical installations and in reading through the on-site guide to prepare a lesson I have come across a section I have...
Replies
4
Views
2K
Firstly, please go easy as I'm still a trainee! Working on my L3 2365 I'm having trouble understanding the rationale behind adiabatics...
Replies
3
Views
764
Hi All, Just looking for some advice: I'm in the process of updating an old cable calc spreadsheet that helps to spit out Zs and Voltage Drop...
Replies
8
Views
867
Now Ive done Periodic Inspection and Initial Virification Qualifications with LCL/EAL (so non C&G 2394/95) # strange part building Modules , this...
Replies
6
Views
936
Does anyone know where I can find the maximum Zs values for AFDD's? Table 41.3 refers to 60898 and 61009-1 but AFDD's are BS 62606
Replies
4
Views
5K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock