was wondering when it comes to an unsatisfactory condition report, then once the corrections are made do you have to redo the form or just add a letter to it stating it is now satisfactory?
 
The EICR will have the faults documented so when the work is done just marry up the new certificates to the report !

Sec F details the recommendations Subject to the necessary remedial action being taken etc!
 
You need to provide either an Electrical Installation Cert or a Minor Works Cert depending on the extent of remedial works completed to eliminate the departures recorded on the EICR. You may also need to inform building control upon completion. A letter stating the defects have been removed is NOT sufficient under BS7671.
 
In this instance you would need to complete a minor works certificate and state on it the departure and EICR serial number.
example. 'Protective Bonding to water carried out to rectify C2 departure of (EICR serial number). You do not need to inform Building Control for this as far as i am aware.
 

Reply to unsatisfactory condition report? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi all, Not sure if anyone can help, but I was wondering how often do shepherd huts need a condition report? I have spoken to the hut supplier...
Replies
8
Views
1K
Seeking advice, we have been replacing extractor fans for a local council and was originally told no ‘like for like’ replacement works needs a...
Replies
14
Views
855
Hi guys, I've gotten AI to write up a terms and conditions for my company and then went through it with AI and tweaked it to make it sound a...
Replies
3
Views
353
I got a TEXT message (i dont know them and i cant find out who they are from the phone number) "Hi speaking from Indeed Are you available to give...
Replies
15
Views
869
Hi everyone Ive just had an electrical condition report conducted on a mixed-use property, and I am extremely surprised that after the last report...
Replies
11
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock