LlandrilloSpark

Evening Fella's

Did an EICR today, on the ring final the r1 and rn were 0.47 and 0.48 but the r2 was >22, every socket had a satisfactory Zs and I also fitted a new RCD board.

The ESC say the broken r2 is a code c2 which would mean an overall unsatisfactory verdict, If it were a live conductor broken in the ring i would fail it but tempted to put it down as a C3, anybody think of a reason why i couldnt?

cheers
 
C2, IMO. you are relying on a single 1.5mm conductor to withstand PEFC rather than 2 . that, in my mind, is a potential danger.
 
Guaranteed the nail to hang the picture will hit the cable with the broken/damaged CPC.
 
I've inspected 70 % of the sockets Trev and found nothing, the house is a tip because of renovation work and I cant access the other 30%, bless the landlady is a little Indian lady and I can see me having a nightmare explaining the whole reason why its not good as explained above!
 
Last weeks was just to freaky......to complicated for a simpleton like me.

I was thinking...

If i measured the fault current to earth at each socket on the circuit, took the highest reading and then used it in the Adiabatic equation, could I then see if the 1.5mm could handle it?, providing I dont find the break of course?
 
Last weeks was just to freaky......to complicated for a simpleton like me.

I was thinking...

If i measured the fault current to earth at each socket on the circuit, took the highest reading and then used it in the Adiabatic equation, could I then see if the 1.5mm could handle it?, providing I dont find the break of course?

Why are you bothering with adiabatic equations whilst doing a PIR ?
Youre there to report faults as found , not redesign around a defect just to get a pass on the cert.
Its code 2 till repaired , end of.
 
Why dont you split the ring at the db and at a socket you think is in the middle of the circuit then get your long lead out and start from there
 

Reply to Unsatisfactory EICR - ring r2 broken? in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Looking at the EICR form. GENERIC SCHEDULE OF TEST RESULTS Looking for clarification on R1,R2,Rn versus r1,r2,rn continuity values. I have...
Replies
9
Views
7K
I would appreciate some opinions on the following situation... I have been asked to comment on an EICR for a local community resource (church hall...
Replies
14
Views
3K
My father In law is selling his property and had a EICR done recently requested by the buyers. I thought the report was not the best quality with...
Replies
23
Views
3K
Hi, I have an Unsatisfactory EICR with the following observations (full report attached, with key details blanked) - the apartment block was built...
Replies
12
Views
6K
Here's one I wasn't expecting on an EICR. Recently rewired and renovated 2-bed property (2015ish). Having an EICR as a new tenant to move in soon...
Replies
40
Views
17K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock