Hello,
New to the forum.
Advice please.
Just run a new circuit of 6mm cable from a 32A MCB, on an additional new CU, which is to run a SPA in a back garden. There is a shut off switch installed for the Spa and an additional fused spur with sockets in an IP rated enclosure.
All readings fine, including IR on L-cpc and N-cpc, which were >299.
However IR on L-N is @ 52M ohms and unstable, i.e. moving up and down, which I believe is indicative of water ingestion into a cable somewhere. It has been very wet during the installation, so this is highly possible. I'm aware that 52M ohms is acceptable, although not ideal on a new circuit.
My question is, the SPA is due to be installed in two days time. Would it be DANGEROUS for any reason to install it before getting a perfect IR reading?

Grateful for any advice.
 
Welcome to the forum Steedy.

What test instrument and at what voltage did you do your IR tests?
 
52Megs is well within any safe limits, it's the 'unstable' bit you've got to decide about. Are you testing just the new cable or is it already terminated at both ends? Maybe you're getting a false reading from a neon in the isolator switch? Low IR between L&N could be a small load or even a surge arrestor connected somewhere. If it was moisture I'd expect to see a similar reading from live and neutral to the CPC.
 
Thanks Gents,
I'm using a Meggar 1553 at 500v for the IR test.
It would be really difficult to break the circuit down as the complicated termination end I put together in my shed and transported it as a whole to site.
If it helps, the circuit has 8m of 6mm internal cable onto another 12m of 6mm SA, when it goes outside. This runs into the cut out switch for the Spa, with 5m of 6mm SA tails running off it loose. From the switch it goes to an IP65 13A switch, with a quadruple socket running off it, housed in an IP rated box. The socket was disconnected for the test as it has a power indication light on it. All materials brand new.
So, it's the fact that the reading is unstable that's potentially dangerous?
 

Reply to Unstable IR reading in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

So was on a call out today and cooker circuit kept tripping the RCD. Disconnected at the board and at the cooker switch and IR’d the cable and...
Replies
9
Views
376
Hi everyone. Hopefully someone can help with a little mystery i had today. The issue is fixed but I want to understand what was going on to help...
Replies
8
Views
595
In my line of work it's very rare that I ever have to change a DB. I'm largely in maintenance; occasionally have to add new circuits etc. so in...
Replies
3
Views
621
Hi, while carrying out an EICR at a farm cottage on Friday i came up against a problem early on. Whilst measuring the Ze the reading i obtained...
Replies
22
Views
2K
A silly fault in a circuit only 4m long is currently eluding me! This is ECIR remedials of a landlords supply in a block of flats. Circuit 2 =...
Replies
3
Views
842

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock