Discuss Unused SWA in the UK Electrical Forum area at ElectriciansForums.net

While we're on the subject:
Socapex plug spider.

Socapex, that wonderful, better than lectriflex, but still a can of worms, pain in the rear end.
Is it rated for 400V or 230V?
Can we run motors through it or can we not?
Should it be 1.5 or 2.5?
Should it be 10A or 16A?
All 6 on one RCD or RCBO's?
Coils, figure of 8, up and down the flyfloor.
 
I suggest they have nothing to do with spare cores in a SWA cable. If you want to use the carry on.

It's not that I want to use them, the industry has hundreds of thousands of them in use and convincing anyone to use an alternative would be impossible.

They have a lot to do with spare cores in an SWA, or any other cable, but with increased risks of accidental contact with the unused cores due to the exposed plug pins.
 
Spiders of both genders are used in entertainment lighting to send six separate 3-wire circuits along an 18-core cable with 19-pin connectors and split them up again at the far end. E.g. it is easier to run ten 18-core cables round a flown truss than sixty 3-core cables.

But, if some 3-pin plugs are energised and others are lying loose, not engaged in sockets, it is possible (and likely) to make contact via the exposed plug pins with unused conductors of cables and multipole connectors in which other cores and pins are energised.
 
That interesting and I would imagine a dangerous arrangement. I can’t see them being used on any of my sites.

As there’s still no consensus on a regulation stating the cores must be earthed. I’ll continue to have the spare cores in SWA cables labelled and terminated into MCC din rails as specified by the designers.
 
There are also permanently-installed variants where a rack of captive cables with plugs feed into tie-circuits to sockets spread around the building, looking very much like a telephone exchange. A lighting fixture would be plugged into the nearest tie circuit, and the corresponding patch plug connected to the desired dimmer channel. In the days when dimmers were expensive, it avoided wasting channels feeding sockets that were not needed for a particular show. Multiple fixtures in widely-spaced physical locations (but lighting the same area) could also be grouped onto one dimmer without running extension cables between them. One might have 72 tie-circuit plugs that could be allocated to 24 dimmer channels each with two sockets.

In most cases those plug tails would be connected to the fixed wiring (usually singles in trunking) by a rail of DIN terminals, with one layer of insulation between the terminal of one plug and that of the next...
 
Socapex, that wonderful, better than lectriflex, but still a can of worms, pain in the rear end.
Is it rated for 400V or 230V?
Can we run motors through it or can we not?
Should it be 1.5 or 2.5?
Should it be 10A or 16A?
All 6 on one RCD or RCBO's?
Coils, figure of 8, up and down the flyfloor.
1605031059546.png

Now I really miss my proper day job ?? ...... feckin' pandemic.
 

Reply to Unused SWA in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi Guys, Had a call out today about an odd issue with a newish Creda DT storage heater. Basically.. Storage heaters were installed in one flat...
Replies
4
Views
755
Hi. Im looking for some advice when calculating submain cables. Basically there is a new connection of 80Amps that is to be used for a dwelling...
Replies
5
Views
350
I am planning to go semi off grid with a victron and battery system. The system will be installed in an out building about 20 meters away from...
Replies
7
Views
709
Was having a poke around the old man's house today. Anyway. DB is under stairs (18th ed following a recent extension. Not done by me but it's...
Replies
7
Views
697
Good evening all, I’m currently part way through my apprenticeship and we are working on IB, IN, IZ and IT and volt drop today. And it got me...
Replies
4
Views
400

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock