the existing setup:
32A mcb, 2 x 2.5mm twin & earth cables in parallel (ring final?) from CU to cooker switch (40m length), there is no other sockets or spurs - only the cooker switch, 6mm cable from cooker switch to cooker (<2m lenght)
it is not right, is it? how can I make it right?
also: the mcb is marked 'heater' not 'cooker'...

Michael
 
What is the cooker rated at and how is the cable routed (clipped direct, through 100mm insulation etc)...? :icon3:

Sy
 
Last edited:
So you're saying there's a ring main like set up, which only supplies the cooker? No that's not right, you'll need to run a single larger cable probably 6mm depending on conditions.
 
Wouldn't say its wrong, just non standard. As long as the cables follow the same route and are of equal length there is not a problem IMO. Label the board correctly, job done.
 
So you're saying there's a ring main like set up, which only supplies the cooker? No that's not right, you'll need to run a single larger cable probably 6mm depending on conditions.

It might be unusual to do, but why couldn't you run a final ring circuit for a cooker if done correctly? Which Regs prohibit this?
 
6kW cooker, 30A max as per manual.
cables clipped on a wooden wall in a ceiling void of 400mmx200mm size, no insulation
my concern is the length of the run ~40 meters
what are the length limits from CU to cooker switch and from switch to cooker? does it apply to this 'ring' or only to proper radial?
wish I would not ask the simple question but can't find answers in the book.
 
Circuit lengths - Appendix 15 BGB
It's also in the Onsite guide and the OSG for the Building Regs (Sorry cant quote either of these as they are in the van).
 
as long as volt drop is within limits, no problem. as truckster said. remember diversity. you're looking at a load of around 16-18A.
 
Seems like a dangerous bodge to me. Parallel cables are usually large sizes that have to be lugged and bolted onto terminals ie impossible for one them to become disconnected. Conversely with 2 x 2.5's its quite likely that a breakage could occur to one 2.5 at a termination point. And your only indication would be when the smoke and flames start.

Should be ripped out and replaced.
 
Seems like a dangerous bodge to me. Parallel cables are usually large sizes that have to be lugged and bolted onto terminals ie impossible for one them to become disconnected. Conversely with 2 x 2.5's its quite likely that a breakage could occur to one 2.5 at a termination point. And your only indication would be when the smoke and flames start.

Should be ripped out and replaced.

same thing can happen on a ring final, but we still install them.
 
True, but I think the large load of cooker justifies my comment. A domestic ring final is unlikely to be anywhere near full load of 32A.
 
As long as all your tests comply then crack on. Just label the CU up and note on cert.

Chances of conductors breaking once terminated and connection units screwed back is going to be rare, if job done right. If Mr or Mrs bodge it DIYer comes along in the future a fiddles, its there problem.
 
with diversity applied, the current is generally <20A, so i can't see a problem.
 
with diversity applied, the current is generally <20A, so i can't see a problem.
the cooker unit would draw a maximum of 29A when all hobs and both ovens are on (and on maximum power).
in normal use it would be 1 oven and 1-2 hobs ~ 10-15A total.
thank you everyone for answers and suggestions.
cables are terminated at mcb and cooker switch and have plenty of breathing space around.
will leave it as it is.
 
If the cooker is only drawing the figures in the region that Tel has posted then it sounds fine.

This is nothing more than a spur off of a ring that is supplying nothing else and all the current is being pulled from the centre of the ring. Perhaps the old ring for the kitchen was used to supply the cooker whilst a new ring was installed for a new kitchen installation?

Surely suggesting a rewire of this circuit could only be made on an OPINION because certain sparks wouldn't be happy installing such a circuit in this manner. However, unless you can PROVE that it is unsafe then you can't really enforce the customer having to stick hand in pocket ;)

:thumbsup
 

Reply to unusual cooker wiring? or wrong? in the Australia area at ElectriciansForums.net

Similar Threads

We have a room in the house that was the kitchen. That has been relocated to a different area, so the old kitchen has been sold off and the room...
Replies
2
Views
615
Hi So converting a 6mm cooker connection point into a 13a unswitched fuse spur with the load being a 2.5mm pre wired cable from a oven . is this...
Replies
2
Views
2K
(Trying again, as picture didn't post first time) Hi, I'd be very grateful if anyone could help me here. Below, I've pasted a sketch showing how...
Replies
5
Views
1K
Hi folks, DIYer here, hoping for some advice before most likely calling in a spark. I'm looking to wire in new cooker and hob (separate units)...
Replies
1
Views
2K
I'll start by saying - I have absolutely no intention of doing any wiring or anything electrical myself. You get someone professional to do a...
Replies
8
Views
822

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock