WDMDL

I'm doing an EICR at the moment for a family member, so most of the remedials are being done as the defects are discovered.
As such, it's gone up to 100% sampling because of what's been found.

The bathroom is upstairs, but the pull cord isolator for the shower is mounted on the WALL.... in the cubbyhole under the stairs!

Now I wouldn't put one there, but I can't actually find a reg that it doesn't comply with, other than the general provisions of 514.1.1 and 530.3.

Any thoughts?

Simon.
 
Pull cord on the wall! Like it!

I guess that needs changing to a switch, as for the location I'm not sure either so hopefully somebody will enlighten both of us!
 
As long as its assessible for maintance reasons i can't see any issues, In the past my firm have installed these in airing cubboards just outside the bathroom for various reasons. Or even next to the Fuseboard!
 
It's almost as good as the perfectly good loop-in ceiling rose...that was full of individual choc blocks!

Maybe they didn't have a small enough terminal driver for the screws?

Simon.
 
If you just change the pull-cord switch to a lockable 50A DP switch or isolator in the cubbyhole please remember as part of complying with 514.9.1 to place a note at the DB detailing the Type, Rating and Position of the switch to inform any spark coming behind you of its location. The switch/isolator needs to be lockable in order to comply with 537.3.1.2
 
Last edited by a moderator:

Reply to Unusual location of pull cord shower isolator - code? in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

This could possible have been a poll, but really just opening up for suggestions and feedback on where folks think an isolation switch for an...
Replies
12
Views
3K
Would be interested to know how people would code this: Upstairs bathroom - with pull cord and shower switch above 2.25 (just)... but over the...
Replies
14
Views
6K
T
Hi, Not new to forums, but definitely new here! I've searched the regs, and guide, long and hard and can't find anything about where a 45A pull...
Replies
87
Views
29K
Hi All, Would appreciate your thoughts on how I might initate a bathroom extractor fan starting. No pull cord starters wanted by the way...
Replies
8
Views
3K
N
I'm putting in an electric shower (7kW), which will be protected (and clearly labelled as being for that purpose) by a 30mA 2-pole RCD + 32A MCB...
Replies
46
Views
4K
Engineer54
E

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock