Hello folks got a quick couple of questions regarding some testing i have recently undertaken.

Im doing an EICR for a friend on a couple of new build flats where the electrics were done by an unqualified builder.

If the install should be done to current regs are things like missing earths at pendants/switchs or no fan isolators a c2 or c3.

Sense tells me a c3 (with a note on the board about no metal light switchs or fiitings) but its a new build where everything should be done to current regs so does that make it a c2?

Theres no chance of connecting the earths as they are burried in a JB somewhere unreachable.

So basically my question is.....if an installation has been completed to the 17th edition when doing an eicr does the install have to meet all the current regs to get a satisfactory result or is it inspected/tested upon its actual condition?

FYI there are numerous small issues that dont really warrant a C2 but at the same time are certainly not up to current regs.

Shouldnt be doing this after the pub, sorry guys :(
 
You are inspecting and testing the installation and comparing that installation to the current regulations and making a professional assessment of whether the installation is safe for continued use, the date it was installed is immaterial, it may help you to realise why some things have been done the way that have but that is all.

You can mention on the covering letter or the current state of the installation that this was installed at the time of 17th edition AMD2 and does not comply, however this is not a reason for changing codes, it does not become less safe because it was built yesterday instead of twenty years ago.
 
You are inspecting and testing the installation and comparing that installation to the current regulations and making a professional assessment of whether the installation is safe for continued use, the date it was installed is immaterial, it may help you to realise why some things have been done the way that have but that is all.

You can mention on the covering letter or the current state of the installation that this was installed at the time of 17th edition AMD2 and does not comply, however this is not a reason for changing codes, it does not become less safe because it was built yesterday instead of twenty years ago.

Thanks for the rapid response.

Thats what i thought but just feels a bit odd.

Whilst i have your attention how would you grade..

Supply tails over 3m without switched fuse and incorrectly supported? (not armoured)?

Thanks
 
Are the tails unlikely to be damaged in any way, e.g. if they run over three meters inside a cupboard and away from anything being pushed against them or hit then they are probably safe and I would code as C3, if they are on an exposed wall in a hallway then they would be a higher risk, non complaint with the regulations and DNO preferences so perhaps a C2, the lack of support would be a C3 for me as I would not really anticipate any fault from tails hanging, so long as they were not pulling straight out of the terminals.
 
I'm assuming that this inspection is to satisfy BCO to get them to issue a completion certificate? Under that situation, I think what I'd be tempted to do would be to code everything as you see fit, make a long list of all the things which are not up to current regs but not necessarily unsafe, and then pick up the phone and have a chat with the BC officer. Tell him that it's fundamentally un/safe (whichever is your finding) but that it's not as it should be and let them make the decision as to what to do about it. They won't be interested in a technical discussion as they simply don't understand our regs, but they will be interested in knowing if something is very/mostly/maybe/no-way safe. They are already on the back-foot as the law says they need to see an EIC, not an EICR (although most are sensible about this).
 
To be honest as these are New Builds there should be no C2s and C3s anywhere on the installation. If there are, there is absolutely no excuse for them to exist, especially no CPC at light fittings/pendants and switches. No fan isolators being provided should be telling you something. To my mind all deficiencies and omissions found on a New Build should be rectified at the installers cost. Putting limitations on accessories and or usage on a New Build is a total nonsense....
 
So basically my question is.....if an installation has been completed to the 17th edition when doing an eicr does the install have to meet all the current regs to get a satisfactory result or is it inspected/tested upon its actual condition?

!!!!!!!!!!!!!!!!!!!

Sounds like the job is one great big F up, with a saunter of cowboys riding around!
 
As Engineer says this is a absolute joke. Its a new build everything should be up to current regs with no limitations.Tell your friend its upto him to put things right and its his own fault for using a unqualified builder to do the electrics on this project. Ridiculous.
 
Get the builder back, drag him back by his balls if necessary. Make sure Building Control have an officer there at the same time, give builder your report telling him to put it right at his own expense and get LABC to prosecute.
Get your councillor involved and the local press. Kick up a stink about it, write to your MP.
Make sure something happens to this clown.
How the hell can someone put a building up without involving LABC? They must have been involved somewhere along the line. Someone has dropped the ball on this, they should be made to make sure it's picked up without any cost to the home owner (unless they were in on the whole load of **** in the first place)
A new build failing to meet current regs? I've never heard anything so ridiculous in my life.
 
Get the builder back, drag him back by his balls if necessary. Make sure Building Control have an officer there at the same time, give builder your report telling him to put it right at his own expense and get LABC to prosecute.
Get your councillor involved and the local press. Kick up a stink about it, write to your MP.
Make sure something happens to this clown.
How the hell can someone put a building up without involving LABC? They must have been involved somewhere along the line. Someone has dropped the ball on this, they should be made to make sure it's picked up without any cost to the home owner (unless they were in on the whole load of **** in the first place)
A new build failing to meet current regs? I've never heard anything so ridiculous in my life.

Gan on son ..... Gerrim telt!!!! ;)
 
There's been a few examples of this lately and I'm bloody sick of them. How can LABC issue a completion certificate without electrical certification?
It's just not possible!
If it's happened either someone has lied their way through things or LABC have not got a bloody clue what they're doing and therefore are unfit for purpose.
 
There's been a few examples of this lately and I'm bloody sick of them. How can LABC issue a completion certificate without electrical certification?
It's just not possible!
If it's happened either someone has lied their way through things or LABC have not got a bloody clue what they're doing and therefore are unfit for purpose.


Anything is possible if you chuck enough moolah at it.
 
But none of that is the job of an electrician. Yes, I'm in complete agreement that it's a bunch of pants and shouldn't be happening, but it's not the job of the OP to go stringing a builder up, that's what BC get paid for.
 
But none of that is the job of an electrician. Yes, I'm in complete agreement that it's a bunch of pants and shouldn't be happening, but it's not the job of the OP to go stringing a builder up, that's what BC get paid for.
I agree but if not him then who? The home owner is the obvious choice but the OP has a more detailed technical knowledge so his input would be understood (and probably ignored) by BC
 
If that's what you have found on the service what is hidden, you said that you could not get to junction boxes so have they been terminated correctly. A loose connection in one of them and you have a fire on your hands + if its a new build I don't think you would get away with an EICR in needs to be and installation cert that you can not do because you did not installed it (Catch 22), as said its a new install so should be no coding any deviations should be rectified before the installation is put into service. I agree With Trev Get the Builder back
 

Reply to Unusual predicament testing 17th Edt install in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Just had an EICR done and C2 (dangerous) applied to 3-way consumer unit which is exclusively for 3 x Storage Heaters. Pic below. Yes its plastic...
Replies
24
Views
2K
Good day. First time poster. We recently had an electrician perform the EICR, as this is a newly purchased property I thought'd I would have the...
Replies
7
Views
692
Hi All I’m in charge of the maintenance (machinery and facilities) in a plastics manufacturing business. I have a ‘team’ of little old me and an...
Replies
3
Views
1K
I've started to move over to AMD 2 forms for my CU installs, if only because the schedule is so much easier to tick and I can stop sticking labels...
Replies
4
Views
1K
Background Two weeks ago, lightning struck a tree in our yard. Many circuits tripped and several electronic devices failed. There was a strong...
Replies
2
Views
858

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock