Good evening all . I am hoping someone can shed some light on a reoccurring problem in a mains room we are working in .

The problem being the UPS modules display a general wiring fault whenever the ATS switches from generator back to mains .

So far the UPS manufacturer and generator company cannot find a cause for the problem . The fault is only displayed when switching one way .

TNS earthing system on both sources with a reference spike for the genny .
 
Is it 3-phase and/or a bunch of UPS in parallel?

My suspicion would be the neutral is isolated during the switch over and they are seeing N-E volts going high on leakage. Try putting a 60W or smaller light bulb between UPS feed (i.e. output of ATS) N-E and see what happens during a test switch-over.
[automerge]1594674201[/automerge]
Another possibility the the ATS change-over contactor is not opening/closing all lives on 3-phase sufficiently simultaneously, but try above and let us know if it reveals anything.
 
Last edited:
Is it 3-phase and/or a bunch of UPS in parallel?

My suspicion would be the neutral is isolated during the switch over and they are seeing N-E volts going high on leakage. Try putting a 60W or smaller light bulb between UPS feed (i.e. output of ATS) N-E and see what happens during a test switch-over.
[automerge]1594674201[/automerge]
Another possibility the the ATS change-over contactor is not opening/closing all lives on 3-phase sufficiently simultaneously, but try above and let us know if it reveals anything.

Yes it is 3 phase with 2 x 30kva ups running in parallel . The neutral has to be switched to satisfy g99 .
 
Yes, most ATS will switch neutral for that reason. However some systems are not happy with a floating 'IT' supply during any prolonged change over so they recommend a transformer or similar between the ATS and UPS to ensure there is the N-E link on the secondary (UPS feeding) side so no floating supply but without violating the general rule on no TN-C supply arrangements (which hard linking N & E on the ATS output / primary side would create).

Also a delta-star (or zig-zag) of transformer can help control 3rd harmonics and lower Zs for the UPS supply loads, so there can be other reasons for looking at that. Specialist companies such as R Baker (Electrical) Ltd can make transformers to specification if needed.

Another possibility is the switch-back from generator to mains is "too fast" in the sense the UPS isa not recognising it as a break but as a glitch on the supply voltage/phase. Some ATS controllers have various programmable parameters and it might be possible to set a defined gap of 0.1s or similar for going back to the mains.

But really the UPS supplier should be able to explain what triggers the "wiring fault" message in the first place!
 
Last edited:

Reply to UPS Fault in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I need your help please once again in tracing a fault. Am DIY but not clueless. Converting former kitchen into 2 rooms: bathroom and laundry. The...
Replies
24
Views
2K
Hi, My alarm system is a Texecom control unit (Premier 64-w) + Keypad + Sounder, and is using the wired zones 1-4 only, with no additional...
Replies
2
Views
2K
Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
Hi Guys, Had a call out today about an odd issue with a newish Creda DT storage heater. Basically.. Storage heaters were installed in one flat...
Replies
4
Views
743
Hello all, First of all I apologise if this is in the wrong forum, I figured the general forum may be the best bet :) Thank you for taking...
Replies
3
Views
469

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock