Hi,,

Well I have few quistions Regarding test results with Fluke 1653.

1. Insulation Test Results for new ring L-N 500M Ohms L-PE 500M Ohms

Are these result normal, 500M Ohms quit high resistance?

2. Test Result PSC 887A and PFC 742A.

3. Functional Testing RCD 30mA.

X 1/2 NO Trip and reading appear 2000mS
x1 trip and reading appear 37.1mS

How do i record them on form?


Any Help or explanation will be grateful...
 
Last edited by a moderator:
Hi,,

Well I have few quistions Regarding test results with Fluke 1653.

1. Insulation Test Results for new ring L-N 500M Ohms L-PE 500M Ohms

Are these result normal, 500M Ohms quit high resistance?

2. Test Result PSC 887A and PFC 742A.

which one shall i record on the certificate and how,, beacuse on form it's says _________kA.

3. Functional Testing RCD 30mA.

X 1/2 NO Trip and reading appear 2000mS
x1 trip and reading appear 37.1mS

How do i record them on form?


Any Help or explanation will be grateful...

1. the fluke i think only measures up to 500Mohm so thats fine.

2. You record the higer of the 2, which in this case is 887/ 0.88kA.

3. not sure about 2000ms. Does it trip with this reading? Either way it shouldn't trip at all with only 15mA test current, which is what 1/2 is. x1 is fine as you have up to 200ms.
 
37.1ms.

Thats it.

You should get a reading to record on your test results with each type of test, and that is what you record.

However, on the 1/2 test it wont trip and therefore maybe shows a reading greater than (>) 2000ms.

Not familiar with the multi testers im afraid!
 
I'm not sure I follow you momeebuilder, 37.1ms is the result of your test. Thats how you read it, it took 37.1 ms for the rcd to trip at 30ma. If it took 200ms it would read that and the same for 300ms.
 
Not sure you should even be testing......understanding and interpreting the results is absolutely necessary....if you are struggling with the units and have no idea of the limits I fail to see why you are doing the testing in the first place....
 
Well practice makes man perfect. :)
No one born with skills.;)
I am student and learning some practical skills at my home..:rolleyes:
Filing out some copied forms...:eek:
All I need help to do things right...:(
Cheers
 
Last edited by a moderator:
Maybe you should consider doing a recognised course......not sure I would be messing about with electricity without some decent level of knowledge.....
 

Reply to Urgent Help in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Hi everyone. Hopefully someone can help with a little mystery i had today. The issue is fixed but I want to understand what was going on to help...
Replies
8
Views
554
Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
Hi Can anyone clear up or explain in a bit more detail what could potentially be causing the results I have. I have just tested a 32a ring main...
Replies
7
Views
1K
Hi, I would love some help understanding an issue I’m having on a 16mm SWA cable running from the CU in my house to the CU in the shed. I believe...
Replies
15
Views
2K
Hi All New to this forum, have read the posts on here from google but only recently signed up. I'm having some issues and some input would be...
Replies
13
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock