OP
craig1000
Customer will not go for reinstalling cable be it a new sub main or an additional cpc.
As we know cpc is too small. What options do I have other than walk away?
Could really do with the work! Can i do CU change & upgrade & then put that circuit back on a 50 amp MCB & make a note on cert of the situation. I could put it on RCD side of split way main CU & then at least although the cable doesn't comply it & its sub circuits have additional rcd protection. Looked further into loft & its confirmed to be used by guests staying over & it is literally a room with a shower room, far from a self contained flat.
100amp main switch with 3 mcbs, 50 for shower, 32 for ring & 6 for lights.
Shower is only a 8.5kw so could reduce 50 to a 40. Realistically the load from that board is never gona get anywhere near the 50amp mcb i will put it on, shower ramped up maximum drawing full 40 amps all lights on & 3 twin sockets, which will have nothing more than a tv/dvd player plugged in & sockets realistically wont be on whilst shower in use. I know this doesn't comply & is in correct I am just trying to see if there is anyway I can do the job & note the bits that don't comply on cert. Any work Iv done /will do will comply other than the fact i have transferred the 16mm into new CU.
As we know cpc is too small. What options do I have other than walk away?
Could really do with the work! Can i do CU change & upgrade & then put that circuit back on a 50 amp MCB & make a note on cert of the situation. I could put it on RCD side of split way main CU & then at least although the cable doesn't comply it & its sub circuits have additional rcd protection. Looked further into loft & its confirmed to be used by guests staying over & it is literally a room with a shower room, far from a self contained flat.
100amp main switch with 3 mcbs, 50 for shower, 32 for ring & 6 for lights.
Shower is only a 8.5kw so could reduce 50 to a 40. Realistically the load from that board is never gona get anywhere near the 50amp mcb i will put it on, shower ramped up maximum drawing full 40 amps all lights on & 3 twin sockets, which will have nothing more than a tv/dvd player plugged in & sockets realistically wont be on whilst shower in use. I know this doesn't comply & is in correct I am just trying to see if there is anyway I can do the job & note the bits that don't comply on cert. Any work Iv done /will do will comply other than the fact i have transferred the 16mm into new CU.