Hi,
This is the scenario;
The kitchen is now converted into a bedroom and there is a bathroom adjacent to that bedroom. The client asked me to re-route the 6mm cable and install a electric shower in the bathroom.
This is what I proposed to do:
10mm would be ideal but 6mm is what I am given to play with.
Please, guys, let me know if I am being over ambitious!
Cheers!
This is the scenario;
The kitchen is now converted into a bedroom and there is a bathroom adjacent to that bedroom. The client asked me to re-route the 6mm cable and install a electric shower in the bathroom.
This is what I proposed to do:
- 8.5KW shower (8500/230=37 amps)
- 6mm T&E cable (current carrying capacity 46 amps, reference method C - Table 6E1 On-site Guide)
- 40A MCB
10mm would be ideal but 6mm is what I am given to play with.
Please, guys, let me know if I am being over ambitious!