Discuss Using meter tails for distribution circuits in the UK Electrical Forum area at ElectriciansForums.net
Hello,
Been asked to do some work in a building consisting of 5 flats which are being redeveloped. At the minute, the distribution circuits to each flat consist of a 60a switch fuse with a 10mm CPC and 25mm line and neutral cables usually used as meter tails.
They are all in trunking and the developers want them either buried in the wall or boxed in.
First question, are "meter tails" OK to be used for distribution circuits?
Second question, I guess they need to be RCD protected - what is the best way of achieving this when each flat will have it's own 30ma RCD. A time delayed 100ma RCD? (which from my interpretation wouldn't meet the requirements, but neither would a 30ma RCD (discrimination) or omitting an RCD on the distribution circuits).
Thanks a lot for your help!!
Yes you can use sheathed singles if you want
No they can't be buried without additional protection
No you can't use a 100mA RCD as additional protection
No you can't use a single RCD to protect the whole installation
Thanks for the replies.
Don't think I could guarantee they'd be >50mm all the way.
So what's the standard way of achieving the required 30ma RCD protection for distribution circuits, while keeping discrimination with the individual flats RCD's? I don't understand how it would be possible lol :confused:
Install SWA so the distribution circuit doesn't have to be RCD protected.
There is no requirement for RCD protection on distribution circuits
I have had to use 25mm double insulated mains tails over a distance as a sub main before now, and due to the difficulty in the run couldnt use SWA, and couldnt rcd up front either so in the parts i had to chase in the wall i run it in 32 mm galv conduit with a lug fixed to one end then bonded back to met
this was only done in straight lenghts i wouldnt try adding bends etc
Reply to Using meter tails for distribution circuits in the UK Electrical Forum area at ElectriciansForums.net
Hello Need to replace a distribution board in the next few weeks to allow for more circuits to be installed in January. Existing is a TT system...
Good morning all, I am currently working on a House in Multiple Occupation (HMO) consisting of 10 flats, with three parking spots equipped with...
Hi, I was hoping someone with a little more insight might be able to shed some light on a potential issue I have, as I can't seem to find another...
7K
I'm doing a college design project and need to choose a suitable range of circuit protective devices for the whole contact. I've chosen and...
For context i am in my 2nd year in college and my head is going round in circles a question in my project for which i need to select the right...
4K