Hi everyone,
Just been on a new build (one off build not cookie cutter), original sparks left some SWA for a car charger and electric gate that I have been working on, I have signed off these two new circuits.
The tails have been taken from a DNO supplied main switch, TN-CS with 100A fuse. He has used 16mm SWA cable and the run is roughly 5 or 6 meters.
Is there any justification for using 16mm instead of 25mm
Also thought the DNO don't like you using their fuse to cover any more than 3m of tails.
If it were me I would have come from the DNO main switch with 25mm meter tails into a 100A DP switched fuse, then perhaps you could use 16mm right? Or am I being pedantic, 16mm SWA's current carrying capacity is high enough so who cares?!
How would you guys do it? Cheers
 
then a isolator should have been fitted .
I reading as there is one provided, That or OP is mixing phrases 'DNO Main Switch with 100A fuse" to be reads it as isolator present otherwise it's just DNO Fuse.

Service head/cutout/DNO Fuse to Henleys' to. Switched fuse than the SWA sub main is how I believe it should go?
 
Sorry if I've not made it clear.
DNO have provided the cutout/head/fuse, to meter, to an isolator.
The spark then used a wiska box directly below the meter cupboard to terminate the SWA and then it pop's out the top of the wiska into the cupboard without any glands but you can't really get at it as they are about as close as you can get them, there is a small gap as those inbuilt meter boxes have those annoying angles sides, then SWA goes directly into the DNO's isolator and MET.
Hopefully thats clearer.
Cheers
[automerge]1583878144[/automerge]
Service head/cutout/DNO Fuse to Henleys' to. Switched fuse than the SWA sub main is how I believe it should go?

Yes, exactly how I imagined it, would you then use 16 or 25 after the switched fuse?
 
I would say the swa conductors are not suitably enclosed. Regardless it requires circuit protection and in your general domestic property 16mm is likely to be adequate with suitable circuit protection.
 

Reply to Using SWA for tails. in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi all, Customer has an extension and this compromises existing meter position, DNO is extending incomer and putting meter box on a different...
Replies
3
Views
359
I am planning to go semi off grid with a victron and battery system. The system will be installed in an out building about 20 meters away from...
Replies
7
Views
680
On a new build site how/ why are people getting away with installing meter tails over 3metres in length and behind dot and dabbed walls with no...
Replies
7
Views
2K
  • Locked
My house was built in the 1930s, The fuse in my service cut out is 60Amp and the wire coming from the street has a 16mm2 copper core(easy to see...
Replies
12
Views
541
Incoming supply on our job comes into the building and then the tails from which go into a switched isolator with 200A fuses fitted. No idea...
Replies
5
Views
933

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock