Hi Guys
Client wants 3 wall mounted under-the-unit sockets for washing m/c, dishwasher and tumble drier. There is a lightly used ring cct available above the units. He doesn't want 3 isolation switches above the units due to having a stainless steel splash back and there's no access below.

Is it acceptable to put one 32 amp isolation switch in the ring and feed a radial from the switch to the 3 sockets via 4 sqmm T&E?

It's not a solution shown on the pretty diagram at the back of the Regs, but I don't see why not?

Cheers

Pete
 
Why not put a 3 gang module away from the steel splash back and feed the sockets from there
 
get him to fit castors to the machines so he can drag them out to isolate.:mad:
 
Hi Guys
Client wants 3 wall mounted under-the-unit sockets for washing m/c, dishwasher and tumble drier. There is a lightly used ring cct available above the units. He doesn't want 3 isolation switches above the units due to having a stainless steel splash back and there's no access below.

Is it acceptable to put one 32 amp isolation switch in the ring and feed a radial from the switch to the 3 sockets via 4 sqmm T&E?

It's not a solution shown on the pretty diagram at the back of the Regs, but I don't see why not?

Cheers

Pete
Yes that’s very helpful – why not reply to Piratepete post more obliging, rather than being silly!
There you go Tel consider yourself severely chastised lol
 
Yeh watch out Tel - Tinks been here for 12 posts - BACK IN YOUR BASKET!
adolph hitler tried . nobody else has come close. my mam was pregnant and was hit by one of them V1 flying bombs. went straight in 1 ear and out the other.
 
The 4mm shouldn't be overloaded if clipped direct, it can handle 37A, and I assume the OCPD is a 32A breaker. However, it would overload the point of the ring where this 'branch' originates from, hence why I wouldn't do it. Just extend the ring and forget about isolators!
 
Not likely to be used at once I wouldn't have thought.

And the each will have their own power use pattern, so you'd need to be unlucky to get all 3 running and running their max current at same time.

FWIW at mine it turns out kitchen and utility room was wired on one RFC and it supports kettle, toaster, micro, dishwasher, washer, dryer and a big fridge. I've not said anything to family and they just get on and jam. I did confirm it is a proper ring and the mcb is not cooked, yet :)
 
And the each will have their own power use pattern, so you'd need to be unlucky to get all 3 running and running their max current at same time.

FWIW at mine it turns out kitchen and utility room was wired on one RFC and it supports kettle, toaster, micro, dishwasher, washer, dryer and a big fridge. I've not said anything to family and they just get on and jam. I did confirm it is a proper ring and the mcb is not cooked, yet :)
we got all that (except for washer/dryer) plus half the downstairs sockets all on a 16A MCB radial. never tripped except when a vivarium heat lamp blew and took out the MCB.
 

Reply to Utility Room Sockets in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I'll start by saying - I have absolutely no intention of doing any wiring or anything electrical myself. You get someone professional to do a...
Replies
8
Views
779
Hi everyone, I have recently had an extension built with a new Utility room. The electrician has put the sockets for the washing machine and...
Replies
22
Views
5K
  • Locked
  • Sticky
Beware a little long. I served an electrical apprenticeship a long time ago, then went back to full time education immediately moving away from...
Replies
55
Views
5K
Hi there, I have two isolation switches above a kitchen workcounter. They currently turn off the power to a pair of unswitched sockets which are...
Replies
2
Views
3K
Morning All I recently completed my first re wire and board change, (with help from the owner who is a gas fitter and plumper, who works with my...
Replies
0
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock