jimmer

I'm just about to start and wire a load of refurbished industrial units which have offices at the back but no natural ventilation. Aparently you need 10 l/s per person per office of extraction. The problem is i have to allow fresh air to replenish the used air, but the only place for inlet / outlet grills to the out side are about 2 meters above the office ceiling so a air brick at low level is not possible. Has anyone else come accross this type of problem and is there some king of dual unit fan that extracts and replaces the air.
Any help much appreciated.
 
You don't need a dual unit fan that extracts and replaces the air. An extractor fan would do this if the airflow is powerful enough. You'll just need to put the extractor in backwards. It will then push air into the room rather than pulling it out, so you'll get clean air for the office. If you mount it in the usual way it will draw the air from the industrial unit into the office.

1 litre/s = 0.001 meters³/s
10 litres/s = 0.01 meters³/s

per hour (multiply by 3600):
36000 litres/hour = 36 metres³/hour

A 4" toilet extractor fan will push 85 m³ into the office, which would be ok for an office of 2 people. Ventilation & Cooling - Extractor Fans, Desk Fans and Air Conditioning

A 4" Manrose MRK In-Line Centrifugal Duct Fans is capable of 180m3/hr 50 litres per second. Enough for 5 people in the office (which I would guess is plenty for any industrial unit), but is a little more expensive. 100mm Inline Centrifugal Extractor Fan

I would mount them outside the office due to noise (or else it will be like sitting in a toilet) and use ducting to vent to the atmosphere. Don't forget about vibration if you mount them directly on the office roof.

I am not an expert, but I hope this helps. I am sure somebody else with more expertise will be able to help further.
 

Reply to Ventilation for an office with no windows in the Industrial Electricians' Talk area at ElectriciansForums.net

Similar Threads

Not specifically electrical, but best way to minimise condensation in a shower room. Asking for a customer. Background. Customer is a neighbour...
Replies
9
Views
1K
Hi, After a bit of advice regarding extractor fans for a dental surgery. Due to the ongoing Coronavirus crisis I've been asked to install...
Replies
9
Views
3K
Hi guys I could not find a suitable place for my question so I wanted to post it here. I have a kitchen extension coming up and I wanted to deal...
Replies
35
Views
11K
P
Been ask by the building firm I sub for to find some regulations about office ventilation and air exchange in habited offices, I told him that...
Replies
12
Views
6K
steve k
S
Hi folks, This is my first post on EF,so go easy on me please ;-) I'm having issues with an inline extractor fan I've installed at my own home...
Replies
8
Views
6K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock