Exactly. You would not IR test only one of the L/N conductors, so why only check loop resistance of one?

The only conductor we are required to check continuity of during testing is the CPC, the R2 test is sufficient for this and acceptable, an R1+R2 test is more normally carried out because it is easier, and it checks polarity at the same time.
[automerge]1598267779[/automerge]
The thing that is confusing me is how does performing only a R1+R2 on a radial socket cct (and operating switches to make sure it breaks) confirm polarity.

The R1+R2 test proves two things, the continuity of the CPC and the polarity.

If the polarity was reversed then you would not get a reading as there would be no continuity.

Remember the polarity test is confirming that L and N are the right way round.
 
Last edited:
The only conductor we are required to check continuity of during testing is the CPC, the R2 test is sufficient for this and acceptable, an R1+R2 test is more normally carried out because it is easier, and it checks polarity at the same time.
[automerge]1598267779[/automerge]


The R1+R2 test proves two things, the continuity of the CPC and the polarity.

If the polarity was reversed then you would not get a reading as there would be no continuity.

Remember the polarity test is confirming that L and N are the right way round.
The OP's point was that if L and E connections at a socket outlet are reversed the R1+R2 test will not indicate that, it may only be apparent when EFLI tests are carried out, in which case a dangerous fault will be energised before being discovered.
 

Reply to Verifying polarity on radial ccts in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hey there, Sorry I’ve just joined up. I’m a qualified electrician/Electrical engineer. Recently sat my 2391-52. My question is I had a fault...
Replies
4
Views
1K
Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
Hi, looking for some ideas on this. I went to an address on Tuesday following a storm where property has been struck by lightning. When the...
Replies
3
Views
716
Morning All I recently completed my first re wire and board change, (with help from the owner who is a gas fitter and plumper, who works with my...
Replies
0
Views
1K
Afternoon all. Bear with me on this one... Despite having been involved in the electrical industry for many years, I'm only just about to embark...
Replies
15
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock