Hi guys,

i have changed a fuse board today in a outbuilding/large shed (it has a kitchen and shower and lounge etc.. a )

It is a TT system with earth rod.

My ZE reading was 187 ohms - now the regs state I am ok upto 200, so I assumed this was ok.

All the R1 + R2 and insulation resistance came back normal.

When I carried out the ZS tests, the reading were very high, for example:

Shower circuit on a 40a MCB - 2.6 omhs !
Kitchen Ring on a 32a mcb - 2.7 omhs !

same for lounge and bedroom rings.

I have checked to regs and these figures are over the maximum allowed.


Any advice ???
 
max. Zs is 1667 ohms if 30mA RCD fitted to all circuits.
 
I checked the date first but it's not April 1st.

What Zs readings would you expect on such a system with an Ra value of 187 Ohms?

Your bonding will have reduced Zs already but RCD protection will give you much higher max Zs figures depending on RCD ratings (up to 1667 Ohms for 30 mA)

You really need to brush up on the reg's before you undertake such work, clients are paying for your competency and skills...
 
teletrix. just to confirm, you are saying the my readings were acceptable ? I understood that (on page 103 of osg) my maximum ZS for a type b 40a Breaker is .093 ohms. ?? The reading i got was 2.6 ohms ??

where are you getting the 1667 from ?

thanks
 
My ZE reading was 187 ohms

So far so good,its after that you are losing the plot

Clue for research purposes only
Its a TT system with a 30 m/amp rcd

Very Hi ZS Reading on TT system? any advice {filename} | ElectriciansForums.net


 
Ok, so on page 50 on the regs, is states that the max ZS is 1667 for TT, so does page 103 of the OSG not contridict this ?

Sorry, but i am a bit confused......
 
Sorry and everything, but oh my god! You quite obviously don't really understand what your doing! If you had 180ohm odd as a Ze, then theres no way in hell your going to get 2.6 ohm Zs!! Zs will never be lower than Ze
 
Hi srl-8 If you cannot get get your Zs down to meet disconnection you can employ an RCD but remember touch voltage 1667 x 30mA = <50V (Touch voltage).

Also remember disconnection in TT is less than a TN system i.e. 0.2s vs 0.4s - 411.3.2.2

Plus are the figures correct - remember Zs = Ze + (r1+r2) so Zs cannot be lower than Ze...
 
Last edited by a moderator:
Sorry and everything, but oh my god! You quite obviously don't really understand what your doing! If you had 180ohm odd as a Ze, then theres no way in hell your going to get 2.6 ohm Zs!! Zs will never be lower than Ze
yes it will, due to parallel paths via the bonding of gas and water. lead pipe is a bloody good earth.
 
Sorry and everything, but oh my god! You quite obviously don't really understand what your doing! If you had 180ohm odd as a Ze, then theres no way in hell your going to get 2.6 ohm Zs!! Zs will never be lower than Ze


Sorry Richard, but I have to disagree with you. From my experience a ZS on a TT system is more often than not lower than the ZE. This is due to parallel paths through water and gas services.
 
To be fair, the OP hasn't mentioned anything about bonding. But yes, i'd aggree that more often than not, a TT system with a lead water pipe will he significantly lower Zs's than the Ze.
 
Sorry Richard, but I have to disagree with you. From my experience a ZS on a TT system is more often than not lower than the ZE. This is due to parallel paths through water and gas services.
yep...at a house we were at recently.....Zs (at the board) through the gas and water services was in the region of 80 odd ohms....there was no earthing (rods or otherwise) to this installation other than what was being provided by the afore mentioned services.....
 
yep...at a house we were at recently.....Zs (at the board) through the gas and water services was in the region of 80 odd ohms....there was no earthing (rods or otherwise) to this installation other than what was being provided by the afore mentioned services.....

Yes, sorry I was trying to demonstrate a completly different point!! and completly aggree with wwhat you say!

Excluding Earth bonding for a second, the Zs cannot be lower than the Ze..correct? which I think the OP didn't understand.
 
assuming that BONDING not earth bonding..that dont exist mate......anyway assuming that main bonding conductors were not in place then a Zs should be higher than a Ze....but never forget the ability of parrallel paths to bring a measured value down....
 
agreed, but with bonding connected, your Ze effectively comes down from say 180 ohms to , in this case, around 2 0hms. this also means that the pefc will flow mostly through the bonding rather than the rod.
 
New posts

Reply to Very Hi ZS Reading on TT system? any advice in the Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock