Good evening all!
I was on site today relocating a consumer unit in a domestic property and got a hefty whack of a CPC...
I have never seen this much leakage in 20 years of work. It is a TNS system, the main switch was off (I got a whack of a gas bond). I am unsure what to do with the situation?
I have attached a video, feel free to reply!
  • IMG_5510.MOV
    52.2 MB
I would contact the DNO as soon as possible. While it might be TN-S at the cutout it might well be fed off a TN-C system with a dodgy PEN somewhere else.
It is hard to see any other explanation of such a high "leakage" current.
agree ^^^. seems like a fault current rather than leakage.
Out of interest, what voltage was measured between the bonding cable and earth?
it's them gas bods getting even for you not bonding to the external meter.
Apologies, in the video was the main earth to be attached to the incoming cable.
The gas bonding connects directly to the consumer unit.
No load on in the house yet the main earth was arcing when connected to the incoming cable.
I’m returning tomorrow to finish the job so will energise / test then.
That's not leakage, that's a flood. Keep us posted on what you/DNO find out to be the cause..
Reminds me of the 'electrified' driveway gates I had at my old house (new build at the time), due to damage to underground street lighting cable, only became apparent when ground was wet. Not fun.
If this place has a lawn out the back, I'd stick a spike into the ground, well away from everything, run a single cable into the house and measure, with an AC volt meter, what potential there is between the DNO earth terminal and your wire, and the bond wire and your wire. Should give you an idea of which bit the fault lies with.
I'd love to see you get the rod back out again ?
Reply to Very odd current through earthing. in the UK Electrical Forum area at ElectriciansForums.net
2nd fixing some sockets in an office today and we were talking about high integrity earthing, I've not got a clue what the sockets are going to...
Please can someone explain if this is a TNCS or a TNS earthing arrangement because it looks like both to me. Old undersized main bonding conductor...
Hi all, Would like some advice on the below. Context: Rural French domestic installation TT system Earth rod is situated inside the property...
As the title says, I am looking for a recommendation for an enclosure and gland arrangement to electrically isolate or divorce the earth/armouring...
5K