Evening all,

Went round to a clients house and did some tests on an outdoor socket. At the junction (in an IP rated wiska box) between the cable coming in from the house and the SWA running to a single outdoor double socket down the garden, the IR test between L-E fails at 0.05 Mohms. When the ends of both cables are disconnected from each other, and the IR tests are done on each cable separately (L-N, L-E, N-E), everything passes! It's only when I test between the earth coming from the house and the line of the SWA that I get the 0.05Mohms. The SWA is being supplied by an FCU inside the house off of a kitchen ring. Supply is TN-C-S.

Any advise much appreciated!

Red
 
Evening all,

Went round to a clients house and did some tests on an outdoor socket. At the junction (in an IP rated wiska box) between the cable coming in from the house and the SWA running to a single outdoor double socket down the garden, the IR test between L-E fails at 0.05 Mohms. When the ends of both cables are disconnected from each other, and the IR tests are done on each cable separately (L-N, L-E, N-E), everything passes! It's only when I test between the earth coming from the house and the line of the SWA that I get the 0.05Mohms. The SWA is being supplied by an FCU inside the house off of a kitchen ring. Supply is TN-C-S.

Any advise much appreciated!

Red
The fault is not between L and the CPC then, it is between L and true earth. Is the armour of the SWA connected to the CPC at either end?
 
This is now solved. Armour of SWA wasn't connected to CPC on either end, and upon further testing found that there was continuity between L and armour of SWA. Turns out L and SWA armour were acting as a path to earth, hence the reading between L of swa and cpc of cable from the house. Turns out @Pretty Mouth was right. Thanks for the help.
Well done. Out of interest, how/where was L touching armour?
 

Reply to Very strange IR fault - any one seen this before? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

A silly fault in a circuit only 4m long is currently eluding me! This is ECIR remedials of a landlords supply in a block of flats. Circuit 2 =...
Replies
3
Views
843
Hi everyone. Hopefully someone can help with a little mystery i had today. The issue is fixed but I want to understand what was going on to help...
Replies
8
Views
599
  • Question
Hi there, I’m a new member to the forum and felt like I could do with some additional insight into a fault I came across on a call-out at the...
Replies
6
Views
445
Hi all , after some opinions on N-E fault or ring main. After chasing this fault and ruining my bank holiday weekend , ring main IR readings as...
Replies
3
Views
1K
Hi, I would love some help understanding an issue I’m having on a 16mm SWA cable running from the CU in my house to the CU in the shed. I believe...
Replies
15
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock