hey guys
had to replace the VFD on my lathe. running off 240v single phase to 3 phase to control the motor in delta config.
i wired the new vfd up as per the last one, which is a different brand. hooked up active and neutral, then the ground to the chassis screw, when plugged in instantly trips breaker, take off earth and it doesnt trip, if i test between house earth(while disconnected to vfd) and chassis of vfd i get 110volts, i also get voltage between chassis of vfd and active and nuetral while the vfd is running, i havent used or touched the vfd because i dont trust it being live. wondering if this seems like the vfd is shorting to the body of it?
 
Greetings from London. May I clarify a few things with you please?

1. What is the make and model of the VFD?

2. Please take some photos of the set-up to show me how everything is connected together and plugged in.

3. Please show on a photo or drawing how you took the voltage measurements and what test equipment you used.

4. What actually 'tripped'? What is a circuit breaker or a residual current circuit breaker (earth fault detector)?

5. What is the machinery that is being supplied? A picture of the specification plates of the machine and the motor that drives it would be helpful.

6. How did you you set-up the vfd parameters?

7. What is the voltage and frequency of your mains supply?

8. How does you property obtain an earth? I rod in the ground? A conductor or the armouring on the incoming supply?

Where are you in NSW?
 
May I ask what experience you have with VSD's, their could be many issues here from simple to quite complex so need to establish how to respond and how to word the responses to tailor to your experiences.

As above please provide full details of drive and also request you provide the info of what exactly is tripping, is it an earth leakage device or just an standard circuit breaker?

I would also need you to confirm if you bought a model with an integral filter or whether you purchased and fitted one separately or have not done so?
 
Last edited:

Reply to VFD tripping breaker in the Australia area at ElectriciansForums.net

Similar Threads

So earlier this year I obtained a large machine with a couple of 3 phase motors in it, and the rest single phase. I bought a VFD, correctly wired...
Replies
15
Views
2K
Hi all. We have a 120v 20 amp circuit to an accessory dwelling with a run of about 75' of direct bury #12. The breaker keeps tripping even when...
Replies
3
Views
263
I have a 20 amp gfci pool pump breaker that trips only when the pump is off during the night. Pool pump runs fine all day. I turn pump off...
Replies
2
Views
728
Hello, I am hoping this is in the correct forum. To start, I acquired a film processing machine that runs on 3 phase. Now before getting the...
Replies
19
Views
3K
Hi guys, I have recently encountered that my circuit breaker for the upstairs lights keeps tripping. I flick it back on and immediately it trips...
Replies
7
Views
843

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock