Discuss Volt drop and cable calculations in the Electrical Forum area at ElectriciansForums.net

Welcome to ElectriciansForums.net - The American Electrical Advice Forum
Head straight to the main forums to chat by click here:   American Electrical Advice Forum

S

Sav

Hi,
does anybody have a quick or easier way to work out volt drop and cable selection calclations ??
I always refer to the BS7671 and OSG, but wondered if anyone had an easier way to work these out.
Cheers guys and speak soon
Sav
:)
 
Hi

The easy way is to use software, a cable calc takes about 1 to 2 mins, and you can play with the figures untill your happy with the cable size. The way i did it before i had sofware was to calculate max and mins for cable sizes, this can work well for most jobs and is a big help when quoting.

Regards

Regards
 
I would respectfully suggest that you undertake a course that covers this as such a course covers other areas that you would need to know.

Calculating voltage drop is simple if you know the formula and the relevant information such as design current, length of cable and voltage drop per amp per metre of the cable in question. There is no other way to work it out as length and design current are variables - very few calculations will be the same.

You can find voltage drop per amp per metre in BS 7671 or in manufacturers data sheets for specific cables, but I find BS 7671 easiest to use as it covers all scenarios on one page once you have identified the correct cable type and size.
 
Hi Phil


A very hard line reply, suggesting he should go on course, he was asking for short cuts, rule thumb and ways picked up by experience to quicken the process of cable calculations. With experience you can determine a cable size, while on site, then I do the calcs to confirm the size, or if the size could be reduced or increased dependant on design.


Regards
 
Sorry if my post was too harsh but I believe all electricians are trained to work this out and that there is no quick way to work it out.

I don't carry a copy of the regs with me but would find it impossible to work out voltage drop without it.

For example, I know it wont be a problem on 6mm cable under 20 metres at about 30 amps. Wouldn't know at 40 metres and 34 amps. You therefore need to know hpw to work it out and there are other factors that make a rule of thumb difficult with cables in a non domestic scenario.

I think it better to be able to cover all bases and know how to obtain and use the information as necessary. Certainly stands you in good stead in an industry that refuses to stand still !

Apologies if I misunderstood the question.

Just found this though in testing and inspection forum:

Approx R1 + R2 values for 1.5mm T&E are 0.29 ohms / 10 meter run.

1.0mm T&E 0.38 ohms / 10 meter run.

Maybe a few calcs like this might give you a method to have a rule of thumb method - just multiply by the design current to get an idea of the voltage drop?
 
Last edited by a moderator:
Useful In...odt (26.1 KB


sorry cant get the link to work.

Cable
1m
5m
10m
15m
20m
25m
30m
35m
40m
45m
50m
1.0/ 1.0
0.036
0.18
0.36
0.54
0.72
0.9
1.09
1.27
1.45
1.63
1.81
2.5/ 1.5
0.02
0.10
0.20
0.30
0.39
0.49
0.59
0.68
0.78
0.88
0.98
4.0/ 1.5
0.017
0.08
0.17
0.25
0.33
0.42
0.50
0.58
0.67
0.75
0.84
6.0/ 2.5
0.01
0.05
0.1
0.15
0.21
0.26
0.31
0.37
0.42
0.47
0.52
10/ 4.0
0.006
0.03
0.06
0.09
0.13
0.16
0.19
0.22
0.26
0.29
0.32
 
Last edited:
No problem mate, I do tend to size the cables first by experience then I do the calculations to see if they are the correct size. Properly not the best way but it seems to work for me. This is all prior to installation. There is a rule of thumb about the ZS can't quite remember. I Do agree you should do your calculations, must admit you start to forget when you use software all the time.


Regards
 

Reply to Volt drop and cable calculations in the Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock