Scott89
Hi guys I was having trouble working out volt drop. Type in google (Doncaster cable calculator) only a guide not exact but though it may help!
Discuss Volt drop cable calculator in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net
Have you a regs book?Ok could you tell me what that is please ie the 3 numbers X together ?
(Mv/a/m) X design current then divide by 1000
I just don't understand what mv/a/m. Is
Judging by you previous posts you are working as an electrician so how the hell do you not know how to do that fundamental simple sum and what it means? How do you work out volt drop in your circuit design?(Mv/a/m) X design current then divide by 1000
I'm not saying it to make you look little but don't you think if you're working as an electrician you should know how to work out volt drop without having to use a website? The tables are in the regs for various types of cable so look in there and post an example of how you would work it out without the use of a websiteI used a website that does it if you look at top off page I'm not looking to be judged just looking for help so I can understand more. So if you have nothing helpful to say and your just looking to make me look little please don't post answer
Length x Design Current x (Mv/a/m) x Factor(1.20) then Divide by 1000 Trada
Where does this "Factor(1.20)" come from, moose?
The values in the tables are for the cables running at their maximum operating temperature.
You don't need this 1.2 factor for Volt drop calcs.
You can reduce the voltage drop for cables operating at lower temps by using the equation in App 4, 6.1
Reply to Volt drop cable calculator in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net