Discuss Volt drop calcs on ring main in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net
Hi Guys,
I'm not into design etc and never have been really but how do you calculate volt drop on a distribution ring main circuit? Ring circuit say covering a large area supplying various loads/buildings. I was thinking split the ring and work it out as 2 x radial circuits, but 1 radial may have more load on it than the other radial. Thanks
Hi Guys,
Sorry if this a duplicate but I asked a question, HV or LV Ring?
Im confused here!
Your an Electrician and you state your not into design etc - so how do you do your calcs for your installs when your confirming they meet VD requirements, Zs values etc before you buy and install the materials.... its part of the job tbh to design your work first and confirm it complies not install and hope a rule of thumb gets you a good result.
Most of the distribution rings I have worked on have been operated as an "OPEN RING"what you describe as 2 radials
As Pete says, if the configuration of the ring distribution means that it will be open sometimes, you need to calculate the worst possible radial that could be present in terms of length and load.
Im confused here!
Hi Darkwood, I'm not on the tools and when when i was it was only domestic planned by others. But i was asked today by a fellow spark and i couldn't answer. Hence my thought 2 x radials. the question was though for a LV distribution ring ( not open)
Reply to Volt drop calcs on ring main in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net
Hi, I'm looking for a bit of advice on a volt drop query we have in our office. I'll explain the scenario and I would really appreciate any...
Hello, New trainee electrician so sorry if this is a dumb question I feel confident with calculating the volt drop for a ring and radial circuit...
HI All, I am building a new house (self build) and have my part P so am running the cabling. My reading of the regs says that any appliance of...
4K
Hello All and happy new year. Over the holiay I have changed all of my old sockets to some nice new ones and added a couple with usb sockets for...
Hi all. Have an issue i'd love some advice on if anyone would be so kind. Will try to be brief. Thank you!! So, have an intermittent RCD trip at...