Hi Guys

I have a question regarding volt drop.

Some time ago a company I worked for installed wall mounted aircon units around their workshop. They wired them into an existing 2.5mm ring main circuit which was in singles in a truncking. During operation some of the units would cause the protection to trip (MCB's). The reason given for this was that the cable runs were too long causing exessive volt drop and thus more current being drawn from the cct. My question is this: Long able runs will cause exessive volt drops due to the extra resistance of the said long cable runs. If the long cables increase the resistance surely the current delivery capability will be reduced! so how can the aircon units draw more current with this added resistance. Or am I missing something.
 
it,s more likely that the circuit is overloaded by adding the aircon units to the ring
 
The mcb would trip if only one air con unit was running so it wasn't being overloaded.

Normally I would agree: less volts more current. But the less volts is caused by too much resistance in the long cables. More resistance equals less current doesn't it?
 
does not matter why the volts reduce the result will be the same

if it is only tripping with one unit on does that mean it is overloaded?
maybe yes maybe no, depends on the loading of the unit and other equipment on same circuit
 
So how about this: If I have a 230w fillament lamp ohms law says it will draw 1 amp at 230volts right? If I now plug in some long extension leads say 3 x 25mtrs I will have added 75 mtrs worth of resistance and dropped some volts. Will that extra resistance make the the lamp draw more current? my gut instinct says that the current will be reduced not increased.
 
Last edited:
depends on the size of the cable does nt it

the fact is the same current is inversly porportional to voltage ...always
thats why 3 phase stuff uses less current and thus smaller cables
 
simple ohms law here

less volts more current
out goes the mcb
shimples !
With a fixed resistance (say 100 ohms), at 240v current=2.4 Amps. At 200v current=2 Amps, so lower voltage at the load means less current draw.
If you have a constant power output of say 1Kw then to produce this power at 240v you would have a current of 4.166Amps. If you only had a 200v the current required would be 5Amps so in this case you would have a higher current.

In the case of an airconditioner the compressor motor has a current relay which connects the start winding until a certain speed is reached . After that time the relay drops out and the current drops with just the run winding remaining connected. With low voltage the compressor starts much slower which prolongs the time both windings are connected. This prolonged high starting current could be the cause of the tripping breaker. Hence long cabling could cause MCB tripping.
 
Last edited:

Reply to Volt drop effect on appliances in the Australia area at ElectriciansForums.net

Similar Threads

Hi, go easy on me please, I've just returned to the trade, well I am about to, I received my Gold Card last Thursday. I've been gen'ing up for a...
Replies
4
Views
824
Hi All, I have a client who is developing a plot of land for a single house. Currently, their 100 amp service cut-out is in a cubicle fed by...
Replies
7
Views
1K
Hello, this is my first post here. I have a little experience with most types of household wiring through a decade of DIY remodeling, and...
Replies
0
Views
756
Over the last few days, I have stumbled across a number of threads that seem to point to a prevalent misunderstanding. Either that, or I have been...
Replies
6
Views
2K
  • Locked
  • Sticky
Beware a little long. I served an electrical apprenticeship a long time ago, then went back to full time education immediately moving away from...
Replies
55
Views
5K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock