hi im struggling with volt drop , the circuit is 6mm 2core swa , run under ground , 220M long ,supplying a transformer charging batterys for a gate system rated at 5A.
Can anyone help me and give me the formula for the calculation? Thanks:confused:
You need to know load or design current in Amps (Ib), Length in metres (L) and mV/A/m which for 6mm 2core armoured is 7.3.
Then use formula (7.3 x Ib x L) / 1000 = drop in Volts.
(7.3*5*220)/1000 = 8.03. So okay if 5A is your only load and no lights. Max allowable drop is 5% of 230V which is 11.5. Or 3% (6.9V) for lighting.
Assuming the full 5A as the circuit design current (Ib) the calc is as follows......
VD = mV/A/m x Ib x L / 1000, which using your figures gives us......7.3 x 5 x 220 / 1000 = 8.03A. Surprisingly within the tolerance 5% of 230V which is 11.5V.
Reply to volt drop? in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net
Hi everyone, I'm new here and was wondering if someone could help to get my college project calculations right. I'm about to start my 2nd year in...
7K
Just taken deilvery of an Electric Car (Mini Electric) and so doing some research into installing a charge point. Supply is a standard Single...
4K
Hi guys & gals, I gave in and bought the new Megger MFT-X1. Got my hands on it Friday night, had a little play with it, used it at work on Monday...
Hope this all makes as much sense as i can make of it and my "problem" can get sorted via some guru on here... Just a quick background on myself...
Hi All, I’m after some advice. I’ll cut to the chase but I can give more detail if needed. A 400A sub main supply needs to be ran 100m, a pretty...