Pricing up a job in a factory and have to wire in a 3 phase supply, just going to double check my cable sizing i calculate i need to use a 10m cable

Swa cable clipped direct on its own , 35m run feeding a unit needing a 3 phase 20amp supply am i right ? just seems a little on the heavy side ?
 
top of my head 2.5mm is on the limit of VD. 4mm or 6mm is adequate.
 
Thanks David , coming in at a more sensible size now knew that looked far to heavy

- - - Updated - - -

4mm is the baby was some how working on the wrong volt drop allowence
 
Cable type: 70 deg.C Multi (armoured)
Fixing method: Clipped direct

Protection device: CB typeC
Protection rating: 20 A

Cable size: 2.5 mm
CPC size: 2.5 mm
Current carrying capacity of cable in this instance: 25 A

Final circuit: Yes
Ambient temperature: 30 deg.C
Number of cables grouped: 1
The cables are spaced


Voltdrop: 2.62 %
Allowable voltdrop: 5.00 %

Length: 35.0 m
Calculated R1+R2: 0.519 ohms
Calculated Zs: 0.87 ohms
Maximum Permitted Zs: 0.92 ohms

Type of system: TN
Supply: Three phase at 400 v
Ze: 0.350 ohms
Fault current: 0.26 kA

Applied correction factors:
Ca: 1
Cg: 1
Ci: 1
Cc: 1


Using a app I have it says 2.5mm2 is fine, although I would personally use 4mm2
 
with 2.5mm i get vd of (18 x 20 x 35)1000 = 12.6V , just over 5% then you have to allow a bit for the outgoing cable/s on the load side.

sorry, wrong column. 15mV not 18. so VD = 10.5V so acceptable.
 

Reply to Volt Drop in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Hi, I'm looking for a bit of advice on a volt drop query we have in our office. I'll explain the scenario and I would really appreciate any...
Replies
3
Views
594
Client currently has a DB in his outhouse. It feeds a pool pump and an air source heat pump. It is currently being supplied using a 4mm T&E cable...
Replies
9
Views
602
I am trying to understand 3 phase volt drop. I understand single phase VD. Lets say we have a 70 meter run of 35mm, 5 core cable from the supply...
Replies
6
Views
2K
Hi. Im looking for some advice when calculating submain cables. Basically there is a new connection of 80Amps that is to be used for a dwelling...
Replies
5
Views
344
Hi guys. I was a commissiong technician before I retired. Hardware and software industrial automation. Miss the work but not the endless travel/...
Replies
12
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock