I'm in a vineyard. There is a 300m buried SWA from the ccu direct to a 2 gang socket.
I'm getting 247V across N and L at the ccu.... But at the socket I'm getting 100V across E and N and 147 across L and N.
Continuity as a radial tested ok
IR All over 500 M
Please list possible issues here. Thank you.
 
Are there any loads attached at the time of measuring?

What were the continuity results and how did you measure them?

300m is a long way, for what I presume if connecting directly into a socket, is going to be <= 2.5mm SWA.
 
I'm in a vineyard. There is a 300m buried SWA from the ccu direct to a 2 gang socket.
I'm getting 247V across N and L at the ccu.... But at the socket I'm getting 100V across E and N and 147 across L and N.
Continuity as a radial tested ok
IR All over 500 M
Please list possible issues here. Thank you.
What size SWA?
 
How did you check end-to-end continuity? Is the SWA two core or three core?

First thought is a broken neutral or SWA/CPC somewhere along the length of the cable so am surprised your radial continuity checks are ok.
 
Last edited:
Are there any loads attached at the time of measuring?

What were the continuity results and how did you measure them?

300m is a long way, for what I presume if connecting directly into a socket, is going to be <= 2.5mm SWA.
It's 6mm SWA
WAS GETTING 2 ohm continuity r1+r2
Measured with L and N cables removed from socket.
 
As above, if you put any load above a few Amps on that length and size of of cable you're going to get an unacceptably high N-E voltage....
 
As above, if you put any load above a few Amps on that length and size of of cable you're going to get an unacceptably high N-E voltage....
Could you explain that a little please Marvo? I understand why approx 4A is the most you should draw due to VD, but how would increasing the load cause there to be voltage between N-E?
 
In a TN system the potential difference at source should be 0v in an ideal world. A circuit designed to have no volt drop should register 0v between the conductors at its point of utilisation. Once you start getting volt drop you must remember in normal circumstances there is no drop in the cpc but there is in the neutral and this drop will measure a potential difference between the conductors, the higher the drop the higher the pd between neutral and earth.
 

Reply to Volt reading across N and cpc in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi guys. Having a weird problem in a house that has suddenly happened. One half of the ring main has 240ish volts (fluctuates of course), and...
Replies
9
Views
465
Over the last few days, I have stumbled across a number of threads that seem to point to a prevalent misunderstanding. Either that, or I have been...
Replies
6
Views
2K
Just interested in peoples thinking on using the neutral through the earthing system like I came across today. I've come across many wrong...
Replies
10
Views
2K
Hello all, Looking for help here as I've come across a strange call-out today. Bare with me here: Got a call from a customer saying they had...
Replies
13
Views
2K
Looking for some guidance here. I'm currently shadowing a guy and we're testing a new extension on a school. 3 phase TNCS supply from the original...
Replies
6
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock