Hello,
I need some advice, I have wired and fitted 2x down lights with 7w Kosnic LED lamps. These are switched from 3 positions. They are on a circuit suppling 13 other down lights all with LED lamps. (All the wiring is new as it's a renovated house, which I've wired).
Now testing the conductors of the cables with the megger all tests are fine and clear. When the circuit is energised the lights work as they should (I have done this sort of thing before!)
When the light switch is in the off position the lights go off, but then 1 down light starts to flash intermittently.
I have tested at the light fittings and I'm getting 74v with the switch in the off position???!!!???
Can anyone help me with this little set-up? I have been tugging my hair out today trying to figure it out!
It's not a loose neutral, as all neutrals are connected with Wago's (Helacons). And I have taken the light fittings out of the circuit.
I have also had all the switches off and connected the wires together with Wago's but still getting the same voltage.
I'm starting to think I'm going mad, but I know that happened along time ago!
Could it be induced voltage in the 3core between the switches? I have turned off all circuits apart from this one so I know that it's not coming from anywhere else.
If it is induced voltage can I loose it somewhere using something? I have been thinking of ferrite magnets? But I don't know that much about them.
Could it also be the lamps? Has anyone had anything sililar happen to them?
Sorry to go on but it helps to get it down on the screen.
Cheer
Billy
I need some advice, I have wired and fitted 2x down lights with 7w Kosnic LED lamps. These are switched from 3 positions. They are on a circuit suppling 13 other down lights all with LED lamps. (All the wiring is new as it's a renovated house, which I've wired).
Now testing the conductors of the cables with the megger all tests are fine and clear. When the circuit is energised the lights work as they should (I have done this sort of thing before!)
When the light switch is in the off position the lights go off, but then 1 down light starts to flash intermittently.
I have tested at the light fittings and I'm getting 74v with the switch in the off position???!!!???
Can anyone help me with this little set-up? I have been tugging my hair out today trying to figure it out!
It's not a loose neutral, as all neutrals are connected with Wago's (Helacons). And I have taken the light fittings out of the circuit.
I have also had all the switches off and connected the wires together with Wago's but still getting the same voltage.
I'm starting to think I'm going mad, but I know that happened along time ago!
Could it be induced voltage in the 3core between the switches? I have turned off all circuits apart from this one so I know that it's not coming from anywhere else.
If it is induced voltage can I loose it somewhere using something? I have been thinking of ferrite magnets? But I don't know that much about them.
Could it also be the lamps? Has anyone had anything sililar happen to them?
Sorry to go on but it helps to get it down on the screen.
Cheer
Billy