Discuss Voltage drop calcs in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net
C
Cider
Hi
Could someone kindly put me in the right direction for voltage drop in cables.
I have the formula from OSG (mV/A/m) x lbxL divide 1000 but cant get my brain to kick in and piece everything together.
There is very little in 7671 unless im looking in the wrong part.
Do I require tables for the cables.
Many thanks
Cider
volt drop for a given csa of cable is given in app.4 brb. and is in millivolts per amp per metre. so you have to multriply the value from brb by the current, then the length. then as it's given in millivolts, divide bt 1000 to get volts.
big red book, otherwise known as BS7671, the bible, bed time reading for electro fanatics, cash cow for the IET
Assessment of existing is done with the formula..
vd = (R1&RN) x Ib x F
where F=1.20
Just a point, if using Appendix 4, then the assumed temp will be at 70 C/90 C, so no factor required unless adjustments for temp are being made.
Onsite Guide, the Resistances are taken at 20 C, so as Widdler has pointed out correction factor will be required to get from lets say 20 C to 70 C.
Chris
Reply to Voltage drop calcs in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net