Gloster Boy

Hi, (new to forum, first thread)

Trying to get my head round voltage drop and using the calcs in practice.

I have radial circuit - 16 amp MCB on a 30mA RCD - 2.5 flat T+E out of household consumer unit, straight through wall and running in plastic conduit along outside of wall and into garage - 12 meter run.

I want to put a shed up top of the garden another twenty meters away. Using junction box can I extend the existing circuit using 4mm SWA from the junction box to the shed?

The circuit would consist of one single 13 amp socket in garage with fused spur for fluorescent strip light, double 13amp socket in shed, with fused spur for another strip light and two 50 watt lamps on the outside of shed.

design current i've calculated = 13.73 amps

So can I split the calculation in two
i.e.

v drop for 2.5mm part of run : 18 x 13.73 x 12m
----------------- = 2.97 v
1000

+ v drop for extension : 11 x 13.73 x 20m
---------------- = 3.02 v
1000


therefore, 2.97 + 3.02 = 5.99 v

5.99 v drop would comply with regs.

Is this a correct way of calculating this circuit voltage drop? And if it is, is this a safe and compliant installation? I'm sure that better practice would be to run the whole thing in 4mm SWA but SWA isnt cheap.

Or am I completely missing the point?

Sorry to those who may be asleep by now, any responses would be greatly appreciated.

Cheers
 
Welcome to the forum.

If your design current of 13.73A is correct for 3 socket outlets and four light fittings and if this would be the total current taken to the furthest end of the circuit then you have correctly calculated the volt drop.

If you break down the current use to each section this would be more realistic and give better results.
The total current would be used up to the first accessory and then then total current taken by the cable would drop as you get further down the circuit.
The easiest breakdown would be to say current usage in garage and shed would be used for the first section and then current usage in shed only would be used for the second section. Remember to take into account any cables running to the accessories as well.

Can't really comment on the suitable design of circuit that would be for you to determine as the on site electrician.
 
Thank you for your reply Richard.

Its late now but i'll recalculate tomorrow based on your advice and post what I've come up with to see if I've understood.

Cheers for your time
 

Reply to Voltage Drop Calcs in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Hi! Once you've calculated the voltage drop in Volts - you divide by 400V for three phase right? For example: three phase 30kW appliance, 10mm...
Replies
5
Views
2K
Hello All and happy new year. Over the holiay I have changed all of my old sockets to some nice new ones and added a couple with usb sockets for...
Replies
4
Views
763
I am trying to understand 3 phase volt drop. I understand single phase VD. Lets say we have a 70 meter run of 35mm, 5 core cable from the supply...
Replies
6
Views
2K
Hi All, I have a client who is developing a plot of land for a single house. Currently, their 100 amp service cut-out is in a cubicle fed by...
Replies
7
Views
1K
Hello, this is my first post here. I have a little experience with most types of household wiring through a decade of DIY remodeling, and...
Replies
0
Views
766

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock