Discuss Voltage drop calculation in the UK Electrical Forum area at ElectriciansForums.net
M
Missing-spark
Hello everyone just want a little help how you would calculate the volt drop if
230 single phase heater circuit
line & neutral conductors combined resistance of 0.68
Temperature at 20 degrees and load current of 16A?
show calculations
got this in my 2395 today wanna make sure I used the correct method
i ended up with a volt drop of 5.4 or 5.2 can't remember
please help thank you
i did 230 divided by 0.68 multiplied by 0.016
Post up your workings and I'm sure someone will advise you.
With your values that would give you a volt drop of 13 volts which is not acceptable are your r1 rn value correct seems a bit high if it's right you need to increase the case of your cable
- - - Updated - - -
Csa of your cable
That's 3 marks lost then. Fingers crossed for my 2394 exam tonight. I'm good with the calculations just that one threw me cause I didn't have the length or mv/a/m
anyone else do the 2395 yday?
why complicate the issue. just use ohms law V=IR, i.e. 16 x 0.68
16 x .68 = 10.88V then adjust to 70 degrees (conductor operating temperature for 70 degree thermoplastic cable) by multiplying by 1.2 = 13.056V
To see if it falls within the allowable %
(13.056/230) x 100 = 5.68%
Reply to Voltage drop calculation in the UK Electrical Forum area at ElectriciansForums.net
Hi! Once you've calculated the voltage drop in Volts - you divide by 400V for three phase right? For example: three phase 30kW appliance, 10mm...
Hello, New trainee electrician so sorry if this is a dumb question I feel confident with calculating the volt drop for a ring and radial circuit...
Hello, this is my first post here. I have a little experience with most types of household wiring through a decade of DIY remodeling, and...
Hello im currently doing the 2391 online I have failed 4 times but I realise there are variations to the voltage drop calculation could someone...
4K
Hi Folks I've been trying to work out whether a doorbell will work with approximately 16m run of bell wire. I've tried to find out volt drop...
7K