Discuss Voltage Drop Equation in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net
N
Noob2013
Hi,
I've been doing some revison and came across 2 different equations for voltage drop.
The first one is;
Vd = mV/A x Ib x L divided by 1000
The second one is;
Vd = (R1 + R2) x Ib x Multiplier
The multiplier is to compensate the difference in conductor temperature at the time of the test and the normal operating temperature of conductors when maximum resistance. 1.2 multiplier for 20 Degrees Celsius.
Are these both correct?
mV/A/m in the first example. this is taken from bgb or osg tables.
second example is basic ohms law V=IR. ( with the multiplying factor for temp. taken into consideration.
Hi,
The first one is;
The second one is;
Tel has explained it well, so i wont expand. But i will give you a couple of whys and what fors.
The (mV/A/M) x Ib x L /1000 would be the calculation used by the designer at the design stage of a new installation.
Method 2, (R1+R2) x Ib X 1.2, this would be used on a periodic inspection and test, when the tester would need to do the calculation and the circuit length is not known.
The 1.2 is to account for the temp difference between the live conductors.
Cheers............Howard
That needs expansion! :)
they will expand as they warm up.i'll get my coat. :waving:
Hi all in the forum
I was browsing his thread, andas the OP appears to be a student I thought I would correct the errors beingmade in the answers regarding the second formula. The first is perfectlyok for calculating volts drop but the second is not. R1 is the resistance ofthe line cable ad R2 is the resistance o the cpc., therefore R2 is not part ofthe volts drop calculation. It should be replaced with Rn (the resistance ofthe neutral cable). The 1.2 multiplier is used in a 70 degree thermoplasticcable to take into account that the cable could be loaded to itsmaximum current carrying capacity. I believe that R1+R2 equations canbe used when evaluating Zs
Hi all in the forum
well spotted there. should be Rn. however the tabulated value of R1+R2 can be used where the cpc is the same size as the line conductor, e.g. with SWA or singles.
Reply to Voltage Drop Equation in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net
all currently working towards my 2391 c&g I&T . I know how to calculate v.d. but the mock test I found online seems a bit out of date or I'm...
Hi! Once you've calculated the voltage drop in Volts - you divide by 400V for three phase right? For example: three phase 30kW appliance, 10mm...
Hi All, Just looking for some advice: I'm in the process of updating an old cable calc spreadsheet that helps to spit out Zs and Voltage Drop...
I am trying to understand 3 phase volt drop. I understand single phase VD. Lets say we have a 70 meter run of 35mm, 5 core cable from the supply...
Hi there, I'm Currently doing my design calcs for my college project and doing the actual Zs calculation. Formula is Zs= Ze (or Zdb) + (R1+R2)...