Hi, iv changed an outside light for a customer and completed all the necessary tests. After powering up I got 230v between L and N but strangely 120v between L and E. The tests were done at the jb prior to the light fitting. Any ideas what could be causing this?

Thanks in advance!
 
What were the results of your Earth loop impedance test?
What results for R1 + R2
You tell us you done all the necessary tests so please post your findings then we can better assist you.
 
What voltage was showing on your tester when you carried out the Zs? As my tester show the voltage between conductors and wont allow me to carry out the test unless the voltage is within a certain range (unsure what it is)
 
Ensure you have good contact to earth with probe ...some items are coated with anti corrosion and can give bad contact, check all termination points again and re-do the testing .... see if you are presented with same situe as it dosnt really tally - your results show a good earth, you say you have 230 L/N yet it seems to show a bad earth L/E.
 
The fault you have described, 120 L-E points towards a loss of earth, but as you say you have carried out the tests and got good readings! When you go back I'm sure the fault will be staring at you in the face.. Please let us know what you find. Theres too many threads where we miss out on the final find
 
Just to update you all.. Went back, retested and strangely all was fine. L to E 230. Only thing I can think is what dark wood said and the connectors where possibly coated throwing my tester off! Cheers guys
 
You said you had 230 L/N and the reading for ELI and R1/R2 were fine so all pointed to a bad lead on tester or poor contact....if this re-occurs elsewhere replace test leads and have meter calibrated or new voltage tester.... either way always best to carry a back-up like a cheap multi-meter.... just because the computer says yes it dont mean its ok all the time.
I had a multimeter that showed 430v to earth on a 3ph system and turned out to be a fault on meter.
 

Reply to voltage query in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

A BG fused connection unit, with neon. A boiler. Fuse out. Spur switched off. I was checking polarity after a colleague had 2nd fixed it and...
Replies
7
Views
710
Hi everyone. Hopefully someone can help with a little mystery i had today. The issue is fixed but I want to understand what was going on to help...
Replies
8
Views
555
Hi all, We have a limited in house PAT testing requirement and were advised that the TIS700 fitted our needs. The unit works fine for 110V and...
Replies
0
Views
639
Hi All, I've installed a Lorex doorbell recently, but it is not turning on. I did some tests using a multimeter and this is what I found...
Replies
5
Views
975
Hi all , after some opinions on N-E fault or ring main. After chasing this fault and ruining my bank holiday weekend , ring main IR readings as...
Replies
3
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock