230V single phase supply.
6amp Lighting circuit, T&E 1.0/1.0
Readings
Highest r1+r2=1.72
IR: L-N, L-E, N-E all >299 Mohms
But when energised there is voltage reading across the conductors at the board as follows:
N-E 112V
L-N 107V
L-E 107V
Then at the light fittings:
N-E 127V
L-N 240V (closed circuit)
L-E 7V

The voltage readigns were taken with Line and neutral terminated at MCB and neutral bar respectively but with CPC/Earth not connected at Earth bar.
The circuit does not trip when energised.
Any thoughts of why this is occurring?
 
Firstly why did you test the voltage with the CPC disconnected?
Secondly, think about what you havent done, and why you are experiencing the problems that you are.
Thirdly think about what you have done again, and why this might stop the circuit from tripping if there is an earth fault!

You should be able to answer your own questions if you think about it.

Cheers..........Howard
 
There had been a unit swap (not by me) and the installer called me as they had got a belt of the CPC. that is why I tested as I did.
I can only think that it is a polarity problem as I get continuity with earth and IR readings are really good.
But I tested all Perm lives at fittings, so if it polarity must be connected incorrectly within voids or walls.

All other circuits test off fine.

I know without earth connected there will be no earth fault.
 
Last edited by a moderator:
where did he get a belt off the cpc? consumer unit end or at the light? if hes changed the CU and the lighting circuit worked fine previously then its something hes done, maybe nicked a cable when screwing the CU up?
 
Con unit
I was informed reason for unit change was that there had been fusing issues. But the information I have received regarding this, so far is vague.
But if cable nicked, I would expect IR issues!
 
he sounds like he doesnt have a clue. id be checking everything again, if hes stupid enough to do that god knows what else hes done.
 
May sound scary but I wasn't there at the time. So don't know the reason behind this, just know that he got a belt, which then led me to testing as I did.
 
he sounds like he doesnt have a clue. id be checking everything again, if hes stupid enough to do that god knows what else hes done.

Well that is a fair assumption, I did disconnect all the circuits and reinstalled, without the aid of any pre-planned EIRC and a young family with pregnant mother complaining about the heating and Jeremy Kyle being off.
All other circuits tested off fine.
This is genuinely not a wind up.
 

Reply to Voltage reading puzzle in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Hi everyone, When checking my consumer unit voltages with the full board off, I stumbled across something head scratching. Measuring the feed...
Replies
1
Views
581
Hi, I would love some help understanding an issue I’m having on a 16mm SWA cable running from the CU in my house to the CU in the shed. I believe...
Replies
15
Views
2K
Hello All and happy new year. Over the holiay I have changed all of my old sockets to some nice new ones and added a couple with usb sockets for...
Replies
4
Views
741
Hi Sorry to bring this one up again but have read numerous posts and answers and not got an answer specific to my situation. I have a Loncin...
Replies
8
Views
2K
Over the last few days, I have stumbled across a number of threads that seem to point to a prevalent misunderstanding. Either that, or I have been...
Replies
6
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock