Discuss Volts drop in the Electrician Courses : Electrical Quals area at ElectriciansForums.net
Hi.
You need the mV/A/m value for the particular cable from the tables in appendix 4 of BS 7671, the (Ib) (design current) of the circuit (not just the fuse/MCB rating), and the length of the circuit. Multiply these 3 figures together and divide the sum by 1000.
Maximum permitted volt drop is 3% (6.9V) for lighting circuits, and 5% (11.5V) for all other circuits.
hi, why do we use the sum of 1000 to divide by?
thanks
Reply to Volts drop in the Electrician Courses : Electrical Quals area at ElectriciansForums.net