This is going to sound stupid but when testing the continuity of bonding conductors does everyone else connect a lead to the met then test the from the lead to the cable?
Discuss wander lead in the UK Electrical Forum area at ElectriciansForums.net
This is going to sound stupid but when testing the continuity of bonding conductors does everyone else connect a lead to the met then test the from the lead to the cable?
This is going to sound stupid but when testing the continuity of bonding conductors does everyone else connect a lead to the met then test the from the lead to the cable?
Test between each end of the bonding conductor with supply isolated and conductor removed from MET
And im probably the only person that has a proper R2 lead aren't i...
thing is though....at college they told us to disconnect at the BS951....and conduct the test to the MET....I was taught to DISCONNECT the bonding at the MET, crocodile clip onto end of cable with a long wander lead and at the pipework end ALWAYS probe onto the pipework NOT the cable clamp, if you get a satisfactoy reading through the pipe you are deffo good, if you probe onto the clamp you arent testing the actual connection through the pipe.
SIMILARLY YOU ALWAYS DISCONNECT AT THE MET TO REMOVE THE POSSIBILITY OF FINDING A ROUTE THROUGH OTHER PIPEWORK ETC EVEN IF YOU DO NOT HAVE CONTINUITY IN THE CABLE YOU ARE TESTING
thing is though....at college they told us to disconnect at the BS951....and conduct the test to the MET....
but how the hell is this proving the integrity of the BS951?...
crackers innit...
Agreed. And im probably the only person that has a proper R2 lead aren't i...bet everyone just uses a self-made one(nothing wrong with that), but what can i say, i like to waste money on tools/equipment + it looks abit more professional aswell
2.5 I'll have you know! lol the best thing I noticed about the proper jobbies is that they lay flat on the floor rather then singles which are a right trip hazard,No chance, wouldn't be seen dead walking about with a drum of 1.5 singles like a lot of cheap skates like to.
thing is though....at college they told us to disconnect at the BS951....and conduct the test to the MET....
but how the hell is this proving the integrity of the BS951?...
crackers innit...
well City & Guilds must be sending out one set of rules for colleges....and another for those offering the 2391...or whatever it is now....The test is to prove conductor continuity, so the test should be performed between both ends of the conductor. The connections at both ends of the conductor do not need to be included. Your thinking along the lines of an IR test between MET and extraneous pipework??
the 0.05 ohms is the reading you should get between separately bonded services, e.g. water to gas. the resistance of any bonding cable will depend on it's length and csa. e.g 10mm is 0.018ohms per 10m.